Hello - Went on a call today for a tripped breaker on circuit #2 on a Trane Intellipak. The compressor that was tripping was #2C which only comes on during 4th stage cooling. Compressor did not sound all that great and when the system called for 4th stage - suction pressure dropped down to 30lbs with a superheat of 50. The suction line was not sweating to the 2nd and 3rd compressors - just alittle on the first compressor. The suction line from the evap to the compressors was not sweating at all. I did not get the subcooling - I will next time! However, my head pressure with all 3 compressors running on 2nd circuit was at 290 with oa 86 and dirty condenser coils. Economizer at 9% (minimum). The blower inlet vanes were only at 60% with building pressure being maintained without having to exhaust any. My inclination was to charge the system via superheat, however, the system is a VAV system so I was told I could not charge using superheat.
Does anyone know which is correct - and does anyone have any idea why I would be running such a high superheat if it wasnt low on charge?
2nd part - circuit 1 had an evap temp of 55 with a sat cond temp of 110, circuit 2 had an evap temp of 62 wiht a sat cond temp of 95 - with a supply air temp of 65? Unit would not go lower on its supply air temp. I feel like im missing something and need help finding it! Any and all responses welcome!
Does anyone know which is correct - and does anyone have any idea why I would be running such a high superheat if it wasnt low on charge?
2nd part - circuit 1 had an evap temp of 55 with a sat cond temp of 110, circuit 2 had an evap temp of 62 wiht a sat cond temp of 95 - with a supply air temp of 65? Unit would not go lower on its supply air temp. I feel like im missing something and need help finding it! Any and all responses welcome!