Relative out of range alarm Niagara

1.6K views 5 replies 3 participants last post by  444fox  
#1 ·
Is there a way In Niagara to set an alarm to trigger if to goes more then 5 degrees away from a setpoint, basically alarm if RoomTemp is +- 5 degrees of SetTemp
 
#4 ·
Create logic on a wiresheet to do your comparison. Then have that logic change the state of either a Boolean Writable or an Enum Writable and then put your alarm extension on that "Writable" point.

You should be able to do this with a T-STAT block but you have to know how the differential functions.
 