Hello guys, one of the many ice machines at the casino I work at has been getting a starving txv fault every time it makes ice..but that's what is weird, it seems to not be having any problems at all making ice. I looked at the thermistors and the inlet temp is in normal ranges but the outlet temp is around 130 degrees at all times!! So is this something I need to call service on asap or is something possibly just wrong with the thermistor? In the manual it says the thermistor is shorted at 475 degrees and open at -22 degrees though so I'm assuming it is working properly. I will try to check it manually tomorrow, its in a difficult place. Also, on a couple of my ice machines I noticed during harvest the evaporator outlet temp is the same as the inlet. I figured the temp would drop by the time it got to the outlet. Sorry if these questions are stupid, I'm just a 22 year old maintenance tech with much to learn lol.