Hey guys, been a while since I had a question that I wasn't able to solve just reading through old threads here. This site really helped me back when I was doing market work after 10-15 years of ULT freezers and commercial AC/R.
I've never actually had to try to solve a liquid-hammer issue in my entire career, so I'm a bit out of my depth on this one even if it's a seemingly simple issue. I stopped doing market work about 12 years ago and got back to my scientific-refrigeration roots, and I've spent the last dozen years working on lyophilizers almost exclusively. Unfortunately these things run a vary wide temperature range throughout a cycle, so sizing components maybe a bit messy and that might be the source of my problem. I don't have that schooling, so here I am.. I'm taking care of two newer units that are breaking liquid-line fittings, solenoid mounting screws, etc. (same manufacturer used to build pretty well-made machines, but alas, here we are..) When the solenoids cycle these things are loud enough to be uncomfortable to my ears.
What I've been able to find seems to indicate that it can be a component sizing issue, but that it can also be alleviated with a capped-off vertical pipe to give it a vapor cushion. I'm going to try that today, but I'm honestly not sure it'll do much with a liquid-line temperature well below 0°C. R404a, 200psig head pressure, subcooled liquid temp eventually reaches as low as -40. Thoughts?
Once everything is chilled down to operating temp, these run with suction pressures in the 22-28inhg range using compound compressors (Carlyle 06CC most often), so I don't typically get much support when I'm looking for help sizing components on units like this (even the manufacturer seems to be stumped, considering that they shipped it like this and can't be bothered to respond to my repeated requests for help solving it) My suspicion is that the solenoid valves are likely dramatically oversized, maybe the TXVs and heat exchangers as well. How likely is it that this is the root cause of the hammering?
I've got 20 or 30 HP two-stage compressors feeding Sporlan B6 solenoid valves on several older units that run smoothly. (although the one with 30 HP seems to always have flashing in the S/G until everything gets cold. Maybe that one needs bigger solenoid valves and the TXVs don't settle down until everything is cold?)
I've also got these newer units, one with 20 HP and the other with 30HP compressors, both using Parker RB15E5 solenoid valves for the main cooling circuits, and smaller RB3E3 solenoids for the interstage/subcooling. The quiet/smooth units all use the same size solenoid valves for the main cooling and the interstage circuits.
Looking for a sanity check here, as I've never considered myself an expert but I feel like I'm on the right track.
I've never actually had to try to solve a liquid-hammer issue in my entire career, so I'm a bit out of my depth on this one even if it's a seemingly simple issue. I stopped doing market work about 12 years ago and got back to my scientific-refrigeration roots, and I've spent the last dozen years working on lyophilizers almost exclusively. Unfortunately these things run a vary wide temperature range throughout a cycle, so sizing components maybe a bit messy and that might be the source of my problem. I don't have that schooling, so here I am.. I'm taking care of two newer units that are breaking liquid-line fittings, solenoid mounting screws, etc. (same manufacturer used to build pretty well-made machines, but alas, here we are..) When the solenoids cycle these things are loud enough to be uncomfortable to my ears.
What I've been able to find seems to indicate that it can be a component sizing issue, but that it can also be alleviated with a capped-off vertical pipe to give it a vapor cushion. I'm going to try that today, but I'm honestly not sure it'll do much with a liquid-line temperature well below 0°C. R404a, 200psig head pressure, subcooled liquid temp eventually reaches as low as -40. Thoughts?
Once everything is chilled down to operating temp, these run with suction pressures in the 22-28inhg range using compound compressors (Carlyle 06CC most often), so I don't typically get much support when I'm looking for help sizing components on units like this (even the manufacturer seems to be stumped, considering that they shipped it like this and can't be bothered to respond to my repeated requests for help solving it) My suspicion is that the solenoid valves are likely dramatically oversized, maybe the TXVs and heat exchangers as well. How likely is it that this is the root cause of the hammering?
I've got 20 or 30 HP two-stage compressors feeding Sporlan B6 solenoid valves on several older units that run smoothly. (although the one with 30 HP seems to always have flashing in the S/G until everything gets cold. Maybe that one needs bigger solenoid valves and the TXVs don't settle down until everything is cold?)
I've also got these newer units, one with 20 HP and the other with 30HP compressors, both using Parker RB15E5 solenoid valves for the main cooling circuits, and smaller RB3E3 solenoids for the interstage/subcooling. The quiet/smooth units all use the same size solenoid valves for the main cooling and the interstage circuits.
Looking for a sanity check here, as I've never considered myself an expert but I feel like I'm on the right track.