cold liquid line at condenser

36K views 24 replies 14 participants last post by  1fowlhunter  
#1 ·
Arrived at house to check 18000 btu mini split a/c only that was not cooling. When I turned it on at the condenser it very quickly started frosting up on the liquid line at the valve and upward. The air off the condenser was warm.The low side was 35.{R-22} I didn't know what to do, so I removed the freon and vacuumed and recharged 4#8oz. When I restarted the unit, the liquid line felt as cold as the suction.My pressure was 55 low side and 75 high side.The line didn't frost while I was there. The ambient was 82 and the inside air from the inside unit was 60. I'm thinking bad compresser,but why is the liquid line so cold?
 
#18 ·
I've worked on many of these. Charge to 70psi and go home. There are a few brands that max out at around 60psi, but once u charge to 70 u will be fine. 55 is too low and it would cause your liquid line to frost.While your charging u will notice the ice melt off once the proper pressure is reached.
 
#23 ·
Pull the charge, if its not even close to the label charge find the leak and weigh in the charge. It seems like most of these type units, the basic charge will cover up to 20 -50 feet of line set. Otherwise follow the installation paperwork .
 