    Quote Originally Posted by timebuilder View Post
    So, I get it all back together, and I'm ready for the burn-off. On the initial visit, the unit had fired, but not well. Due to the bad HX, it could not be operated long enough to fully delve into whatever problems might be present.

    I get out the Testo and find the gas pressure to the unit is not what it should be.

    I look at the regulator, and find the setting was screwed down ALL the way, in an effort to get more gas into the unit.

    Now, it has a nice new one. Not screwed down to the bottom, either.

    Attachment 69462

    Maybe these guys are a necessary part of the industry, to keep the rest of us working. It still bothers me, though.
    I thought vent limiters were for indoor use only. Shouldn't there be a goose neck on that regulator vent instead. Or better yet, Maxitrol now makes rubber regulator caps which around here, have greatly helped keep moisture from getting in and freezing up the regs
    Figman

  2. #22
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes

    Cool

    Quote Originally Posted by german 8'er View Post
    I thought vent limiters were for indoor use only. Shouldn't there be a goose neck on that regulator vent instead. Or better yet, Maxitrol now makes rubber regulator caps which around here, have greatly helped keep moisture from getting in and freezing up the regs
    From Maxitrol:
    NOTE: Vent limiters are designed for use indoors and in
    spaces where limiting the amount of gas escapement due to
    diaphragm failure is critical. Vent limiters are not to be
    used outdoors if they are exposed to the environment.
    13A15 vent protector is available for outdoor use when vent
    protection is required.

    HTH,
    Hearthman

  3. #23
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Thread Starter
    Quote Originally Posted by hearthman View Post
    From Maxitrol:
    NOTE: Vent limiters are designed for use indoors and in
    spaces where limiting the amount of gas escapement due to
    diaphragm failure is critical. Vent limiters are not to be
    used outdoors if they are exposed to the environment.
    13A15 vent protector is available for outdoor use when vent
    protection is required.

    HTH,
    Hearthman
    Thanks for posting that excerpt. I saw that as well.

    This is out by route 1 and 202. I'm sure there was an appropriate inspection done when these units were piped in. At least, one would hope so.

    All of the other units for this strip mall are pretty much identical to this one.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #24
    Join Date
    Jan 2010
    Posts
    3
    Post Likes

    help

    been a while since i've been on this site. where do you find the link for the pic??

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •