    We installed a new Carrier Infinity 19 Seer condenser. The control is a Honeywell IAQ. (Furnace is Heil 96% variable spd). The problem is that the condenser will not start/run in low speed. The IAQ is sending 24vac to Y1 on initial call for cooling but condenser does not start (furnace blower engages). Unit runs perfect with power to y1 & y2. If I then pull power from Y2, unit drops to low speed, amps drop about 25%(per Carrier claims) but units shuts down after ~20 sec. No error code noted from LED on Infinity board. Thanks in Advance, Skip Shein
    Quick reply to this message Reply  

  2. #2
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    I assume this is the Infinity 19 heat pump? According to Carrier's product literature on the 25HNA9, "Infinity Control (MUST be used, no substitutes)."
    Quick reply to this message Reply  

  3. #3
    Join Date
    Jul 2009
    Posts
    10
    Post Likes
    Thread Starter
    Unit is NOT a heat pump. Just 2 spd scroll condenser.
    Quick reply to this message Reply  

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    According to the installation instructions, the 19 can only use a standard stat in "emergency mode". I guess that means if your Infinity control dies, you can get some cooling.

    Indoor Thermostat Control Options
    Model Infinity Control Standard 2 ---stage Thermostat
    24ANA7 Yes Yes
    24ANA1 Yes No (Emergency Mode Only)
    Quick reply to this message Reply  

  5. #5
    Join Date
    Jul 2009
    Posts
    10
    Post Likes
    Thread Starter
    Are you saying that even though the Honeywell IAQ has two cooling stages, the Infinity condenser will not function in low unless I purchase a matching Infinity thermostat & control?
    Quick reply to this message Reply  

  6. #6
    Join Date
    Jul 2009
    Posts
    10
    Post Likes
    Thread Starter
    After reviewing installation instructions, I agree that Infinity controller is required. My furnace is Heil VS 2-stage. Will the Infinity controller operate this furnace. Does it also have 24Vac output relays? If not, is there an interface board?
    Quick reply to this message Reply  

  7. #7
    Join Date
    Dec 2001
    Location
    St Louis, MO
    Posts
    196
    Post Likes
    The Infinity thermostat will not work with this furnace. It must be used with an Infinity furnace. There is not an interface. Your only option is to replace the furnace or switch to a different condensing unit.
    Quick reply to this message Reply  

  8. #8
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    OOPS!

    On the other hand, you don't really need that silly control board to run a 2 step scroll in both stages, or even an ECM condenser fan motor in both speeds.
    Quick reply to this message Reply  

  9. #9
    Join Date
    Jul 2009
    Posts
    10
    Post Likes
    Thread Starter

    Confused Use of Y1/Y2 Possible?

    Are you saying the interface Bd can be disabled thus providing control from Y1/y2? Why would they provide traditional G,C,Y1,Y2 connections if it is not possible to use these connections? Again, unit runs perfect on high(y2), Just no start on Y1.
    Quick reply to this message Reply  

  10. #10
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    So, Mark, is there any hope for him or does he need to swap out to the TS model of Infinity that will work with a non-Carrier furnace?
    Quick reply to this message Reply  

  11. #11
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    So, Mark, is there any hope for him or does he need to swap out to the TS model of Infinity that will work with a non-Carrier furnace?
    Beats me, I don't know the Carrier products that well.

    My comment in the previous post was more joking than anything.
    The compressor and fan motor in the outdoor unit could be made to function as a 2 stage unit without the control board. It would likely have some warranty implications, but all that would be needed to "fix" the system is a rectifier and some reconfiguring of wiring.

    The non communicating Trane XL16i straight cooling units use the same Copeland 2 step scroll compressor, and often an ECM fan motor, but don't have a control board at all, just a rectifier to rectify the 24vac from Y2 into DC to operate the solenoid in the compressor.
    Y1 goes straight to the contactor, and Y2 goes straight to the rectifier to energize the solenoid in the compressor.
    Quick reply to this message Reply  

  12. #12
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    I'd say he's sunk on this one. Dealer who put it in needs to make it right, switch to the TS version of the Infinity which will work fine with the Heil and IAQ. OR better yet, put in a matched ICP system that could qualify for the tax credit.
    Quick reply to this message Reply  

  13. #13
    Join Date
    Jan 2008
    Location
    California
    Posts
    110
    Post Likes
    Ran into something similar on same product. Our situation was originally created by retrofit where existing control wire only had three wires available. It later became evident that this condenser needed to see 24v at the condenser C and R terminals, in addition to hitting Y1 or Y2. Several ways to resolve it, we intended to use add-a-wire but mounted dedicated trans in condenser.

    Also learning that Infinity series products don't seem to love the new Honeywell stuff, but that can be worked out to some extent.
    Quick reply to this message Reply  

  14. #14
    Join Date
    Jul 2009
    Posts
    10
    Post Likes
    Thread Starter
    So the refrigerant slide valve solenoid is 24Vdc and is normally de-energized or open in the low speed position? What controls the condenser fan speed? Just power on/off to different winding via a relay?
    Quick reply to this message Reply  

  15. #15
    Join Date
    Jul 2009
    Posts
    10
    Post Likes
    Thread Starter
    Are you suggesting that 24vac be supplied constantly at R,C and then sending another signal to Y1 and Y1/y2 for Low/Hi control?
    Quick reply to this message Reply  

  16. #16
    Join Date
    Jan 2008
    Location
    California
    Posts
    110
    Post Likes
    Quote Originally Posted by skipshein View Post
    Are you suggesting that 24vac be supplied constantly at R,C and then sending another signal to Y1 and Y1/y2 for Low/Hi control?
    In essence, yes. We found that if R, C terminals were not powered, no go. Carrier local tech support helped us, suggest you engage them - each application has it's unique issues.
    Quick reply to this message Reply  

  17. #17
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    forty305

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.

    Your post has been deleted.


    Quick reply to this message Reply  

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •