Hello all. I am trying to figure out a furnace issue. I know it has to do with the pressure switches but before I spend the $X for a new one, I'd like to run it by professionals that have been doing this for a while lol.
My furnace is starting up and shutting down before ignition. I under the pressure switches to an extent. I'm not familiar with my furnace setup though. My other furnaces seem to be just single stage pressure switches. Essentially just making sure that the exhaust vents aren't plugged. However mine has 2 pressure switches. One is connected like normal to the inducer. This is a -.10 WC switch. It tees off to another pressure switch which is wired in series. This pressure switch is -.80. It also has 2 nipples. The first hose comes from the tee from the other pressure switch and the inducer. This one if sucked on I get continuity. Makes sense since that brings it to a vacuum like the inducer is supposed to do. The other hose goes to another tee, which one end goes to the sealed burner box and one to the gas valve. If I blow through this hose I also get continuity.
When I short the switch the furnace turns on like normal. However when I just run the furnace and test the continuity the switch beeps are on and off. Sort of randomly but mostly about half second intervals. I don't fully understand this second switch and I'd like to know exactly how it functions. The first switch makes complete sense. It makes sure there is a vacuum pulled. If there is a blockage or some other issue, there is no vacuum and it cuts off the switch and creates the open circuit for the two switches that are in series. But the second switch having two functions both resulting in closing the circuit just doesn't make sense to me.
I guess my biggest confusion is how this switch works exactly. I can't imagine the intermittent continuity is normal. Idk if that is caused because maybe the inducer is meeting the .80 WC but the pressure required for the other hose connected to the burner box and gas valve isn't met? I do not have a manometer. I'll be ordering one to better service my equipment down the road. I also can't blow and suck on the tubes at the same time to test continuity in those conditions lol. I've attached a rough idea of the setup. Its switch #2 that I'm most curious about. I know that there is atmospheric pressure differential things going on here to make sure combustion is done correctly but I just don't understand how that activates the switch.
I have tested ohms as well on this switch. It varies between 55 ohms nd 62 ohms for what its worth. It dipped as low as 49 ohms though at least within the time my meter updates
My furnace is starting up and shutting down before ignition. I under the pressure switches to an extent. I'm not familiar with my furnace setup though. My other furnaces seem to be just single stage pressure switches. Essentially just making sure that the exhaust vents aren't plugged. However mine has 2 pressure switches. One is connected like normal to the inducer. This is a -.10 WC switch. It tees off to another pressure switch which is wired in series. This pressure switch is -.80. It also has 2 nipples. The first hose comes from the tee from the other pressure switch and the inducer. This one if sucked on I get continuity. Makes sense since that brings it to a vacuum like the inducer is supposed to do. The other hose goes to another tee, which one end goes to the sealed burner box and one to the gas valve. If I blow through this hose I also get continuity.
When I short the switch the furnace turns on like normal. However when I just run the furnace and test the continuity the switch beeps are on and off. Sort of randomly but mostly about half second intervals. I don't fully understand this second switch and I'd like to know exactly how it functions. The first switch makes complete sense. It makes sure there is a vacuum pulled. If there is a blockage or some other issue, there is no vacuum and it cuts off the switch and creates the open circuit for the two switches that are in series. But the second switch having two functions both resulting in closing the circuit just doesn't make sense to me.
I guess my biggest confusion is how this switch works exactly. I can't imagine the intermittent continuity is normal. Idk if that is caused because maybe the inducer is meeting the .80 WC but the pressure required for the other hose connected to the burner box and gas valve isn't met? I do not have a manometer. I'll be ordering one to better service my equipment down the road. I also can't blow and suck on the tubes at the same time to test continuity in those conditions lol. I've attached a rough idea of the setup. Its switch #2 that I'm most curious about. I know that there is atmospheric pressure differential things going on here to make sure combustion is done correctly but I just don't understand how that activates the switch.
I have tested ohms as well on this switch. It varies between 55 ohms nd 62 ohms for what its worth. It dipped as low as 49 ohms though at least within the time my meter updates