    Defrost cycle occurs most often when outdoor temp above freezing & humid???

    I would appreciate confirmation of something I was told from a knowledgeable source since it is a little counter-intuitive (at least to me). It is that the defrost cycle occurs most often when outdoor temp is above freezing & there is moisture in the air, particularly on inverter units such as the Carrier 38MBRB/40MBAA. I am considering this unit due to increased 17F btuh output versus non-inverter heat pumps, and was asking how often the defrost cycle may occur overnight at about 20F. The unit uses condenser pipe differential temperature to determine when to defrost. If indeed it will defrost more at higher temp than lower temp (since colder air holds less humidity), it will not have a large impact when trying to get as many btuh's out of the unit as possible on cold evenings.

    Thank you

  2. #2
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    It is all about runtime, and moisture in the air.
    If the ambient is above freezing, but has a lot of moisture in the air… as in, it’s raining, or foggy. IF the heat is running long runtimes, it will need to defrost more often. If however, the heat doesn’t run long runtimes, the warm ambient, and moisture can prevent defrost… it’s all about how tight and well insulated the home and ductwork is.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  3. Likes Tjune54 liked this post.
  4. #3
    Join Date
    Mar 2018
    Location
    Virginia
    Posts
    5,120
    Post Likes
    If conditions are right, and the coil is developing ice, you can expect about 1 5min. defrost cycle per hour.
    "I think Quantum tunneling would work great... "

    "Call a technician for God's sake. Or we'll see you on the news or the Dark Side of the Moon."

  5. #4
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    You need to look at the COP (coefficiency of performance)

  6. #5
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    And look for a heat pump with demand defrost. Timers should be outlawed.

  7. Likes R600a liked this post.
  8. #6
    Join Date
    Mar 2018
    Location
    Virginia
    Posts
    5,120
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    And look for a heat pump with demand defrost. Timers should be outlawed.
    Yes they should!

    I think the one he’s looking at would be…any higher end unit/good name brand should be
    "I think Quantum tunneling would work great... "

    "Call a technician for God's sake. Or we'll see you on the news or the Dark Side of the Moon."

  9. #7
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    And look for a heat pump with demand defrost. Timers should be outlawed.
    We are looking at you payne / bryant / carrier.
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •