Thread: Trane rauc 402-A New run capacitors but still not running. HELP

  1. #1
    Join Date
    Oct 2022
    Posts
    4
    Post Likes

    Trane rauc 402-A New run capacitors but still not running. HELP

    Not sure on the tonnage I’m pretty sure it’s a 4 ton to be clear. But have replaced 2 run capacitors to compressor and to fan as well. Came on once and fails to do so anymore. Would like to replace contacter too since no power is passing thru when calling for cooling. What type of contactor do you guys recommend, also any other possible issues?

    Checked continuity on the compressor windings, checked voltage to everywhere, only seeing 230 hit the contacter and nothing coming out the other side.

  2. #2
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes
    Are you a tech or is this your unit?

  3. #3
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    We are not going to be able to assist you, being that this a non-DIY site.

  4. #4
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Have you tried changing the evaporator coil yet?

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by hvacvegas View Post
    Have you tried changing the evaporator coil yet?
    Maybe call someone before you get hurt or hurt someone else!

  6. #6
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes
    Lighten up guys, his profile says he's a HVAC Contractor. Let's let him respond to my question.

  7. Likes Mr Bill liked this post.
  8. #7
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    He might of got spooked 👻

  9. #8
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes
    Quote Originally Posted by VTP99 View Post
    He might of got spooked 
    Can you blame him?

    Let's give people a chance. He might just be a green tech, and if so we need to try and help him within reason. I'll move the thread if that's the case.

  10. Likes Mr Bill liked this post.
  11. #9
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    I hear ya I think the guys here are just condition to the never ending homeowner diyer.
    That said yes let's see what is revealed 🤔

  12. #10
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes
    Quote Originally Posted by VTP99 View Post
    I hear ya I think the guys here are just condition to the never ending homeowner diyer.
    That said yes let's see what is revealed 樂
    That's still no reason to be rude. I'm about to start taking member's * away if this continues.

  13. Likes Mr Bill liked this post.
  14. #11
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Agreed

  15. #12
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by Danielm61944 View Post
    Not sure on the tonnage I’m pretty sure it’s a 4 ton to be clear.
    This is a mid to late 1970's unit, and it's rated at 4 tons.
    Instead of learning the tricks of the trade, learn the trade.

  16. #13
    Join Date
    Oct 2022
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by Special-K View Post
    Are you a tech or is this your unit?

    I’m a tech but this my unit, just starting off in the field so please bear with me lol. Came into this new home with a poorly maintained unit from what I learned.

  17. #14
    Join Date
    Oct 2022
    Posts
    4
    Post Likes
    Thread Starter
    Yes lol thank you only been in the field for about a year just started picking up on trouble shooting but mainly installing residential for the most part as of right now.

  18. #15
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes
    Quote Originally Posted by Danielm61944 View Post
    I’m a tech but this my unit, just starting off in the field so please bear with me lol. Came into this new home with a poorly maintained unit from what I learned.
    I'm gonna take you at your word. I've moved the thread to Tech to Tech where we can help you more. AOP is just for homeowners. Please note the new location of your thread.

    Get your post count up and apply for pro membership, that will unlock the Pro areas to you and then we can help you much more.

    https://hvac-talk.com/vbb/threads/11...nal-Membership

  19. #16
    Join Date
    Oct 2022
    Posts
    4
    Post Likes
    Thread Starter
    Thank you I appreciate it, new to the forums.

  20. #17
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by Danielm61944 View Post
    Thank you I appreciate it, new to the forums.
    Can you fill out your profile more with information about you? Make sure you include an email address too.
    Instead of learning the tricks of the trade, learn the trade.

  21. #18
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by Danielm61944 View Post
    Checked continuity on the compressor windings, checked voltage to everywhere, only seeing 230 hit the contacter and nothing coming out the other side.
    So I am guessing you also had 24 volts to the low voltage side of the contactor, but it would not engage?
    Instead of learning the tricks of the trade, learn the trade.

  22. #19
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Danielm61944 View Post
    Yes lol thank you only been in the field for about a year just started picking up on trouble shooting but mainly installing residential for the most part as of right now.
    Start Reading
    Attached Images Attached Images

  23. #20
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Danielm61944 View Post
    Not sure on the tonnage I’m pretty sure it’s a 4 ton to be clear. But have replaced 2 run capacitors to compressor and to fan as well. Came on once and fails to do so anymore. Would like to replace contacter too since no power is passing thru when calling for cooling. What type of contactor do you guys recommend, also any other possible issues?

    Checked continuity on the compressor windings, checked voltage to everywhere, only seeing 230 hit the contacter and nothing coming out the other side.
    What does the caps have to do with the contactor pulling in?
    You should research the make and model of the compressor and find out What cap is recommended.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •