Odd flame sense current readings
I was wondering if anybody else has seen when they’ve tried to get a current reading on their flame sensor the value jumping around between 12 and zero rapidly and anywhere in between.
Originally Posted by
Aceanihilator
Loose ground connection. Could be. That’s the only time I’ve seen that. 12 is quite high though.
If board has a electronic digital segment display, signal will be scrambled like you see. Look in the manual and find the way to check your flame signal through the board. Is it a Lennox unit?
Blake79
If I remember correctly it was a Lennox and did have a segment display. How would you go about checking flame sensor current on a single rod system?
Aceanihilator
Do you happen to remember the model number of this Lennox furnace?
Aceanihilator
It was a EL296UH
Thanks for that information. If you put an email address in your profile, I will send you the service manual on this unit.
Post Likes - 1 Likes, 0 Dislikes
2sac liked this post.
rundawg
Added and Thank You!
Hold in the button next to display until F flashes. Let go andl F symbol shows and than the actual reading will display
Aceanihilator
Check your inbox.