    r422b trane intellipak

    anybody know of any issues using r422b instead of r22 on 100 ton intellipak, making leak repairs, new condenser slab, couple new compresors, rebuild txvs on circuit 2 of machine. it has csha150 scrolls

  2. #2
    Join Date
    Nov 2018
    Location
    Western Maryland
    Posts
    209
    Post Likes
    You are gonna end up with like a 80 ton unit when done but it does run and work. Fairly close to 22 numbers.

  3. #3
    Join Date
    Feb 2005
    Posts
    335
    Post Likes
    Thread Starter
    that much capacity lost ?

  4. #4
    Join Date
    Nov 2018
    Location
    Western Maryland
    Posts
    209
    Post Likes
    I have not seen any large conversion that has not lost somewhere around that. It requires a bunch more gas. I have done about half a dozen conversions over 30 ton as my reference. Someone with more experience will likely be along.

  5. #5
    Join Date
    Feb 2005
    Posts
    335
    Post Likes
    Thread Starter
    ok, thank you

  6. #6
    Join Date
    Nov 2011
    Location
    CO
    Posts
    13,705
    Post Likes
    Not sure if Trane has the CSHA's on the "Do not convert" list......some you can't.

    looking at the data, they are approved for 407C, and would need POE oil, so you may be ok changing those over.

    If that unit has had a bunch of compressors, be aware of the system oil charge, there may be a bunch out in the system.

  7. #7
    Join Date
    Feb 2005
    Posts
    335
    Post Likes
    Thread Starter
    thats what prompted me to ask due to maybe trane didnt approve

  8. #8
    Join Date
    Aug 2022
    Location
    New Jersey
    Posts
    6
    Post Likes
    I did a conversion because of leaks on a 27.5 ton voyager, tandem 3D scrolls. Used 422b and killed both compressors in 4 days. There was a field installed liquid line core drier, opened it up and found metal shavings, definitely not in there when we changed the core after fixing the leaks. Clearly oil return issues.
    Bluon ( tdx-20 ) will give you the best support for a conversion. They will tell you exactly what you need to do because they have case studies of doing them on intellipaks.
    One other note we were replacing a compressor on a R-22 desert-aire, I spoke to them prior to quoting it out and they recommended that I stay with R-22 not switch to Bluon ( tdx- 20 ). I thought that was great, not just telling me to use their refrigerant.

  9. Likes VTP99 liked this post.
  10. #9
    Join Date
    Jan 2010
    Posts
    33,417
    Post Likes
    Yep Trane won't cover warranty if a substitute refrigerant is used with their 3D scrolls.
    Attached Images Attached Images  

  11. #10
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    35,448
    Post Likes
    If you are using 422b on the Trane 3D compressors, you have a high probability of ending up at 50% capacity due to the dead compressors.

    Read the doc attached then look near the center of the compressor label and you will likely see 3D Scroll.


    Name:  3D scrolls & 422B.png
Views: 189
Size:  110.0 KB
    I do a triple evac with nitro to remove non condensables.

    I'm feelin' a little peculiar.

  12. Likes VTP99 liked this post.
  13. #11
    Join Date
    Nov 2011
    Location
    CO
    Posts
    13,705
    Post Likes
    Are the CSHA's "3D" scrolls?

    In the literature for them, they can run POE

  14. #12
    Join Date
    Jan 2010
    Posts
    33,417
    Post Likes
    .
    Attached Images Attached Images  

  15. Likes slctech, 2sac liked this post.
  16. #13
    Join Date
    Nov 2011
    Location
    CO
    Posts
    13,705
    Post Likes
    Well, there you go.....proceed with caution!! LOL!!

  17. #14
    Join Date
    Nov 2018
    Location
    Western Maryland
    Posts
    209
    Post Likes
    And there we have it! Good call on the Trane info fellas... that is all new to me. Luckily, my conversions have all been Copeland or Carlyle semis. The collective input here is why this is the best HVAC forum out there!

  18. Likes BBeerme liked this post.
  19. #15
    Join Date
    Feb 2005
    Posts
    335
    Post Likes
    Thread Starter
    thanks to all

Posting Permissions