Results 1 to 20 of 35
Thread: Intermittent cooling
    Aug 2022
    My AC unit has an intermittent cooling problem. This usually happens in the afternoon or at night, or hot days when the AC need to work for a while. It stops blowing cold air but instead blows warm air inside when the temperature reaches the set temperature. The AC keeps running but not cooling since it blows out warm air. The temperature rises up. I found the outdoor unit does not stop and the condenser fan however blows cool air. After stopping the unit by increasing the set temperature above room temperature for a while, restarting the system will again work normally and blow cold air This happens intermittently and the technician cannot detect any problems because the problem does not show up while the technician is here. One technician sent by the Choice warranty company changed the thermal expansion valve but did not solve the problem. Another one is recommending changing the condenser fan motor, stating it is overheated. It has not been changed yet.
    The unit brand is GrandAire and is only one year old. I am using a Nest thermostat to control the system. The unit is only for cooling. We have gas furnace for heating.
    What could be wrong? Thank you so much in advance.
    Aug 2022
    Name:  When not cooling_inside.jpg
Size:  690.2 KBName:  When not cooling_outside.jpg
Size:  863.8 KBName:  When it works_inside.jpg
Size:  543.1 KBName:  When it works_outside.jpg
    Those are photos showing when it works and stops cooling.
    Jan 2014
    New England
    You got a matched system, meaning both section replaced at the same time and even better a AHRI matched system or an older Air Handler to a new outdoor unit, better known as a Frankenstein system. If older indoor unit, what refrigerant was it using, R22 or R410A?
    The compressor is shutting down for whatever reason, and the outdoor fan still running. You may need a much more experienced Tech. checking your system, as replacing the metering device did not help.
    What’s the model numbers and brand of the indoor and outdoor unit.
    How did your system work last year?
  4. Likes scampbyc liked this post.
  5. #4
    Jun 2014
    Dover, DE
    You lost me at warranty company.
    Often these guys they send are the cheapest they can find. They don’t hire based on skill but instead how cheaply they work.
    Since the fan appears running in your not operating picture it’s likely not the issue.
    You may want to move on from the warranty company and hire out an independent contractor.
    With the warranty company service and terribly unreliable Nest thermostat, it’s enough to drive your unit to suicidal thoughts.
    I havent failed. Ive just found 10,000 ways that wont work. - Thomas Edison
    Its not whether you get knocked down, its whether you get up. - Vince Lombardi
  6. Likes scampbyc, kdean1 liked this post.
  7. #5
    Aug 2022
    Quote Originally Posted by Bazooka Joe View Post
    You got a matched system? or an older Air Handler to a new outdoor unit.
    Thanks! The air handler (coil) is also changed to a new one when they changed the outdoor unit. I'm not sure whether the compressor is shutting down. I need to learn how to check it is off while the fan is spinning.
  8. #6
    Aug 2022
    Quote Originally Posted by rider77 View Post
    Yes, there have been around 10 visits for this problem from three different contractors. I just reset the thermostat and see whether it will work. Thanks for your suggestion, I will look for an experienced contractor.
  9. #7
    Jan 2014
    New England
    Quote Originally Posted by scampbyc View Post
    If the reading is 79 degrees or whatever the outdoor temperatures is exiting the condenser at one point and 113 at another time and outdoor fan is running, then IMO the compressor is shutting off while still calling for cooling. Listen closely when you have the 113 degree rejected air and when it’s at 79 ( or whatever the outdoor temperature is when compressor is not running but fan is ) there is a different sound when a compressor and fan is running and only when the condenser fan is running.
    Note the outdoor temperature when these happen.
  10. #8
    Aug 2022
    If the reading is 79 exiting the condenser at one point and 113 at another time and outdoor fan is running, then IMO the compressor is shutting off while still calling for cooling. Listen closely when you have the 113 degree rejected air and when it’s at 79 there is a different sound when a compressor and fan is running and only when the condenser fan is running.
    Thank you so much. You are right. When the unit works well, the rejected air is 113 degree and there is no noisy sound. But when the cooling is not working, the rejected air is 79 and there is a different sound with some noise from the outdoor unit. The technician told me the fan motor was overheated and need to be changed. But I searched online and found that the motor will stop if it is overheated. In my case, the fan still works.
  11. #9
    Jan 2014
    New England
    Hopefully you registered the indoor and outdoor sections as thinking you will have a 10/10/10 compressor, parts, coil warranty. Not registered chances it reverts to a 5/5/5. California and Quebec need not be registered to receive the manufacturers maximum warranty.
    Didn’t they check the amprege draw of the outdoor motor to see if it was running within specifications? That’s a very basic troubleshooting check.
  12. #10
    Aug 2022
    Thanks! I registered the warranty and have 10-year warranty. I will cancel the change of fan motor. I forgot to mention that another contractor asked me to change the compressor.
  13. #11
    Jun 2014
    Dover, DE
    Why did they want to change the compressor?
  14. #12
    Aug 2022
    They said the cooling is bypassing the compressor and blow cool air in the outside unit. I am not quite getting his point. One thing is he put the wrong wire for the blower fan and burned our blower fan motor. He changed for free because it is his fault. I am guessing he want to take that money by convincing the warranty company to change the compressor so that he can get enough labor charged on me. Just guessing.
    I just found online that the airwave function in nest thermostat may be the culprit. I turned off that function and will update the results several days later.
  15. #13
    Aug 2022
    Thank you, you remind me about the nest thermostat. I found that the airwave function is on, which may be the reason. I just turned it off and let's see.
  16. #14
    Southold, NY
    Loose the warranty company!
  17. Likes scampbyc liked this post.
  18. #15
    Athens, Ohio
    1. Nest thermostat
    2. Home warranty hacks
    3. Using an IR thermometer to measure air temperature
    Site member map HERE!
  19. Likes scampbyc, pacnw liked this post.
  20. #16
    Aug 2022
    Updates on the Airwave function. I reset the nest thermostat and turned the Airwave function. It does not work. The problem still shows up.
  21. #17
    Southold, NY
    Brake the NEST outside and hit it with a Hockey Stick!
  22. Likes Scoff liked this post.
  23. #18
    Mar 2013
    East Concord, NY
    When it is operating correctly put your ear on the little line in the house. You should hear a constant hissing. No bubbling, farting, glurps or anything like that. When it is not working, try it again to see if the noise is missing.
    Nest is POO!!
  24. Likes scampbyc liked this post.
  25. #19
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    The water's not gonna clear up in Washington DC until we get the pigs out of the creek.
    RexP says:
    My neighbor was having a similar problem with his Nest thermostat and heatpump system. Cooling worked much of the time, but occasionally would cycle into heat mode. Sort of a backwards ‘defrost’ mode.
    The {asterisk} output of the thermostat was driving the reversing valve, and for some reason would toggle during cooling. You mentioned that your system “sounds different” when it isn’t cooling properly. When this is happening you might feel the larger of the two copper tubes connected to the outdoor unit. If it is hot then the system is trying to heat your house.
    I am going to assume the thermostat could be made to work properly by someone interested enough to dig into the programming. That someone isn’t me.
    Good luck.
    PHM
    The conventional view serves to protect us from the painful job of Thinking
  26. Likes scampbyc, rexp liked this post.
  27. #20
    Aug 2022
    Thank you! The two copper tubes are not hot. The thicker one is not cold when it is not working, but not hot. The thinner one is cool or cold when it is not working, which is weird.