    Siemens P2 Insight Graphics Error

    Hi All,

    I have an old legacy P2/Insight Siemens system that is displaying "Cab Error" inside black boxes where the points normally load on the graphics. I know this means a cabinet communicate failure of some sort, and have already googled a long list of items to troubleshoot. However, if I click on the black boxes, I can still access, monitor, and control the point. So, I know that network communication is still functioning. Not to mention, all the nodes currently appear latched.

    So, how do wake up these graphics to stop displaying this "cab error" box? What's the trick to these old Siemens systems when they behave this way? In Schneider I would be checking graphics bindings and such. Not sure if this old Insight front end has anything similar. I appreciate any and all help.

  2. #2
    Join Date
    Apr 2015
    Location
    Omaha, NE, USA
    Posts
    126
    Post Likes
    There are no bindings like Schneider Struxureware. You use the full point name in the graphics and it maps it internally. I would check/restart the InsightAsync service and see if that corrects it. A reboot of the PC/Server would also be something to try.

  3. Likes bfam4t6 liked this post.
  4. #3
    Join Date
    Oct 2019
    Posts
    3
    Post Likes
    Thread Starter
    Thanks zmanvortex. I finally got permission for some reboots, and rebooting one of the panels did the trick. I'm guessing this is the rather well documented EEPROM issue. I'm hoping this client just bites the bullet and decides to upgrade this old stuff. Thanks again!

  5. #4
    Join Date
    Jul 2022
    Posts
    3
    Post Likes
    Our branch has this emergency call once a week and we just go and cold start the panel. My understanding from some of the senior guys is this can happen when Insight attempts to reload the database while the FLN communication is banging back and forth. Usually if I get this call I’ll remove the FLN, coldstart the panel and wait for it to load the DB, then plug the FLN(s)

  6. #5
    Join Date
    Aug 2020
    Location
    Washington DC
    Posts
    90
    Post Likes
    I always thought this was a server-side issue, not with the controller itself.

    I've seen this very frequently on a campus with all sorts of network traffic issues. A very poorly operating database. 10s of panels producing thousands of alarms daily (deadband: 0, time delay: 0)
    I thought the panels were glitching, but they were performing flawlessly when I looked more closely using the HMI

    Also, what is this "well documented EEPROM issue"?

  7. #6
    Join Date
    May 2019
    Location
    United States
    Posts
    342
    Post Likes
    Quote Originally Posted by bfam4t6 View Post
    Hi All,

    I have an old legacy P2/Insight Siemens system that is displaying "Cab Error" inside black boxes where the points normally load on the graphics. I know this means a cabinet communicate failure of some sort, and have already googled a long list of items to troubleshoot. However, if I click on the black boxes, I can still access, monitor, and control the point. So, I know that network communication is still functioning. Not to mention, all the nodes currently appear latched.

    So, how do wake up these graphics to stop displaying this "cab error" box? What's the trick to these old Siemens systems when they behave this way? In Schneider I would be checking graphics bindings and such. Not sure if this old Insight front end has anything similar. I appreciate any and all help.
    This means that the front end isn't connected to the panel due to comms or it missing it's configuration.