Thread: Multi Zone systems vs. two pipe VRF system

  1. #1
    Join Date
    Nov 2019
    Posts
    31
    Post Likes

    Multi Zone systems vs. two pipe VRF system

    Good morning. I know a few commercial systems (e.g. Mitsubishi VRFs have a two pipe system from the outdoor unit that runs to each head), but do multi zone systems "share" the refrigerant in a similar way? Or is each zone partitioned off in the out door unit somehow?

    For example, if you have multi zone system made up of 5 zones lets say, with a total of 5 separate line sets running to each indoor unit from the outdoor unit, if there is a refrigerant leak on ONE indoor unit, the entire system will eventually be depleted of refrigerant, correct?

  2. #2
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    Yes, mutizone units share a common refrigerant circuit.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  3. #3
    Join Date
    Nov 2019
    Posts
    31
    Post Likes
    Thread Starter
    Quote Originally Posted by rider77 View Post
    Yes, mutizone units share a common refrigerant circuit.
    Okay thanks. I noticed with one multizone system I installed less than 24 hours ago (2 indoor units), one head is blowing ice cold and the other blowing moderately cold air. My first thought always tends to go to worse case scenario, like "must be a refrigerant leak". More than likely it's another reason. Thanks again.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,730
    Post Likes
    Quote Originally Posted by gpier View Post
    Okay thanks. I noticed with one multizone system I installed less than 24 hours ago (2 indoor units), one head is blowing ice cold and the other blowing moderately cold air. My first thought always tends to go to worse case scenario, like "must be a refrigerant leak". .
    Safe assumption.

  5. Likes gpier liked this post.
  6. #5
    Join Date
    Mar 2010
    Location
    Sunny SoCal
    Posts
    854
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Safe assumption.
    Insufficient information to assume.
    Eric

  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,730
    Post Likes
    Quote Originally Posted by ESokoloff View Post
    Insufficient information to assume.
    I’d make a bet on it!

  8. Likes R600a liked this post.
  9. #7
    Join Date
    Nov 2019
    Posts
    31
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    I’d make a bet on it!
    I hope you’re wrong.

    I’m going to put a leak detector on the only place there could be a leak this afternoon. I can’t get in the space until then. I’ll follow up with results.

    Here’s my question (assuming a leak in fact) why would one indoor unit blow so much colder than the other? Thus my original question.

  10. #8
    Join Date
    Mar 2010
    Location
    Sunny SoCal
    Posts
    854
    Post Likes
    Quote Originally Posted by pecmsg View Post
    I’d make a bet on it!
    It’s a high probability of insufficient refrigerant to the coil that’s not cooling but there’s insufficient info to say the systems short on charge.

    I’m not saying your wrong (low charge), rather saying I don’t (yet) agree based on given info.


    To the OP, follow manufacturers charging procedure to determine if unit is low on charge before looking for leaks that may or may not exist.

    Your issue sounds to be a shortage of refrigerant to the effected coil but that could also be a restriction (filter/strainer or metering device) rather then system under charge.
    Eric

  11. #9
    Join Date
    Mar 2010
    Location
    Sunny SoCal
    Posts
    854
    Post Likes
    Quote Originally Posted by gpier View Post
    I hope you’re wrong.

    Here’s my question (assuming a leak in fact) why would one indoor unit blow so much colder than the other? Thus my original question.
    I don’t have enough information to accurately answer that but I can surmise it possibly be similar to how hydronic (water) heat pump strainers will contaminate the lowest (elevation) one(s) in a building due to gravity.

    The piping to your systems two heads MIGHT tend to direct liquid to one head & mixed phase (liquid/vapor) to the other this shorting it of sufficient liquid.

    You need to check system charge/metering device operation before leak checking.

  12. #10
    Join Date
    Nov 2019
    Posts
    31
    Post Likes
    Thread Starter
    All good points. I will investigate further.

  13. #11
    Join Date
    Nov 2019
    Posts
    31
    Post Likes
    Thread Starter
    Quote Originally Posted by ESokoloff View Post
    I donÂ’t have enough information to accurately answer that but I can surmise it possibly be similar to how hydronic (water) heat pump strainers will contaminate the lowest (elevation) one(s) in a building due to gravity.

    The piping to your systems two heads MIGHT tend to direct liquid to one head & mixed phase (liquid/vapor) to the other this shorting it of sufficient liquid.

    You need to check system charge/metering device operation before leak checking.
    Well, happy to report I solved my problem. Not a refrigerant loss. I did waste about 2 hours today trying to figure it out. What I'm not happy to report is how stupid I am. Let me explain:

    I had my teenage son helping me yesterday. Everything went well, although we worked late, on a Sat night, till about 7:00pm (never a good idea). We started it up, and it worked fine. This AM one unit (like I originally said) was blowing cold, the other not so much.

    This afternoon I used the leak detector. Nothing. Pressure test went well yesterday, triple evacuation, and I held a vacuum at less than 500 for over 2 hours for each zone before I released the refrigerant. All my joints are good. I opened the outdoor unit and the accumulator was covered in heavy frost. One line set was iced over. The other wasn't. Now I'm racking my brain, thinking low on charge from the factory? My line set to each unit is only about 25 ft. (I didn't need to add refrigerant) Is the expansion valve stuck? Or bad? Is it another restriction of some sort? Not looking good. I don't want to spend half the day tomorrow to recover refrigerant and weigh it out to find out it's exactly what it should be. This is a Bosch system, and I've been pretty happy with them. This is the third Bosch I've installed, and the first two were solid and still running fine.

    Note: I assigned my kid yesterday to wire up the communication cables. Wondering if he got the color/number sequence off, I opened up the indoor unit in question, and it was correct. "Red, Black, White, Ground". WHILE I'M LOOKING AT THIS, I hear the other unit in the other room (which is in the "off" position) making a popping noise. I go look at it, and the outside cover is dripping with condensate.

    Now I think I know what it is. I go back to the outdoor unit to see if he got the wires backwards. And he did. He wired zone A to zone B. And zone B to zone A. So the indoor unit in question was calling for refrigerant, but the outdoor unit was sending it to the other unit even when it was off (thus the popping noise and the condensate). Last night, they were both working fine because they were both on full blast, and both calling for refrigerant, so the offices cooled very well over night.

    All that to say, I was happy to find this mistake. Glad it was simple. Certainly can't blame my kid. I should have checked his work. That's my fault for not checking it.

    Anyhow, thanks for reading this far and helping me today. Time for a beer.

  14. #12
    Join Date
    Nov 2019
    Posts
    31
    Post Likes
    Thread Starter
    Quote Originally Posted by ESokoloff View Post
    I donÂ’t have enough information to accurately answer that but I can surmise it possibly be similar to how hydronic (water) heat pump strainers will contaminate the lowest (elevation) one(s) in a building due to gravity.

    The piping to your systems two heads MIGHT tend to direct liquid to one head & mixed phase (liquid/vapor) to the other this shorting it of sufficient liquid.

    You need to check system charge/metering device operation before leak checking.
    Well, happy to report I solved my problem. Not a refrigerant loss. I did waste about 2 hours today trying to figure it out. What I'm not happy to report is how stupid I am. Let me explain:

    I had my teenage son helping me yesterday. Everything went well, although we worked late, on a Sat night, till about 7:00pm (never a good idea). We started it up, and it worked fine. This AM one unit (like I originally said) was blowing cold, the other not so much.

    This afternoon I used the leak detector. Nothing. Pressure test went well yesterday, triple evacuation, and I held a vacuum at less than 500 for over 2 hours for each zone before I released the refrigerant. All my joints are good. I opened the outdoor unit and the accumulator was covered in heavy frost. One line set was iced over. The other wasn't. Now I'm racking my brain, thinking low on charge from the factory? My line set to each unit is only about 25 ft. (I didn't need to add refrigerant) Is the expansion valve stuck? Or bad? Is it another restriction of some sort? Not looking good. I don't want to spend half the day tomorrow to recover refrigerant and weigh it out to find out it's exactly what it should be. This is a Bosch system, and I've been pretty happy with them. This is the third Bosch I've installed, and the first two were solid and still running fine.

    Note: I assigned my kid yesterday to wire up the communication cables. Wondering if he got the color/number sequence off, I opened up the indoor unit in question, and it was correct. "Red, Black, White, Ground". WHILE I'M LOOKING AT THIS, I hear the other unit in the other room (which is in the "off" position) making a popping noise. I go look at it, and the outside cover is dripping with condensate.

    Now I think I know what it is. I go back to the outdoor unit to see if he got the wires backwards. And he did. He wired zone A to zone B. And zone B to zone A. So the indoor unit in question was calling for refrigerant, but the outdoor unit was sending it to the other unit even when it was off (thus the popping noise and the condensate). Last night, they were both working fine because they were both on full blast, and both calling for refrigerant, so the offices cooled very well over night.

    All that to say, I was happy to find this mistake. Glad it was simple. Certainly can't blame my kid. I should have checked his work. That's my fault for not checking it.

    Anyhow, thanks for reading this far and helping me today. Time for a beer.

  15. #13
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,730
    Post Likes
    Been there
    Got the t-shirt!

  16. Likes gpier, Zamoramax liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •