    It's cooling, but obviously well off spec. Txv replaced 3 months ago, performed well up to now. Charge weighed in 3 months ago. Consenser coil thoroughly cleaned today.
    Here are the numbers at 88 outside and 77 indoors:
    400/144
    Sc 25
    Sh 7
    Suction temp 57
    Liquid line temp 93
    Lsat 118
    DeltaT, a lousy 8 degrees
    Condenser fan output seems normal.
    Ideas.
    Sep 2014
    Charlotte NC 28213 USA
    System is overcharged ?
    Check for leaky returned air.
    Where's the indoor unit located ? Attic ?
    Apr 2018
    Air handler in attic, no air leaks, I realize overcharge is #1 suspect, but pretty confident that the charge weighed in correctly.
    Could be a restriction, or a problem with the fairly new txv. This unit has txv's at the evaporator and also at the condenser.
    Could warm the sensing bulb in attic and see what pressures do.
    Could recover 1/2 lb and see where sc goes.
  4. Likes Zamoramax liked this post.
  5. #4
    Apr 2018
    Recover 1/2 lb, sound like a good idea?
  6. #5
    Apr 2018
    Recovered 1 lb of R410a from 2 ton system.
    New readings, but OS temp about 4 degrees cooler.
    380 head, down about 15
    Suct 139, unchanged
    Sc. 21​ ​ to 23, down about 4
    Sh 9- 11, up about 3
    Suc temp 58-59, up about 2
    Llt 92, same
    Lsat 113, down 5
    Delta t, still 8
  7. #6
    Virginia
    Are these symptoms of Heat Strips turning on somehow ?
    I've never seen it myself .... well .... not in the summer ... I saw one stuck in the winter because the fan board relay
    Tell your Cat I said "Psst Psst Psst"
  8. Likes dcipherrva, kdang liked this post.
  9. #7
    Dec 2021
    Richmond, VA
    Quote Originally Posted by Snapperhead View Post
    Welded contactor, possibly, but I’ve also seen it where a T6 stat was installed and emergency heat is tied to W and not AUX/E on the thermostat. For some reason W feeds just enough voltage constantly when the stat is programmed for heat pump operation.
    Few things to check, but I figure someone would probably notice if it’s been 3 months since install.
    Edit: Just read only TXV replaced, unless thermostat was recently installed disregard most of this. My mistake.
  10. #8
    Jan 2005
    Emerald Coast
    Quote Originally Posted by etbrownx View Post
    Suct 139, unchanged
    Llt 92, same
    Lsat 113, down 5
    Delta t, still 8
    Still overcharged, a good chance it's oil logged...do you have an IR camera or visual or evap?
    Do not attempt vast projects with
    half vast experience and ideas.
  11. #9
    Jan 2012
    Missouri, USA
    No mention of airflow. Static pressure, return and supply wb/db.
  12. Likes Tjune54 liked this post.
  13. #10
    Jul 2009
    South Carolina
    The pressures are off but not enough to cause an 8° TD so I suspect you're picking up heat somewhere.
    I don't know what type of system you have but you could just pull the disconnect to the outside unit during a call for cooling & check the supply temp.
    That's one way to see if you're picking up heat from the blower unit.
    Gary
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
  14. Likes R600a, kent_a, Tjune54 liked this post.
  15. #11
    Sep 2014
    " The pressures are off but not enough to cause an 8° TD so I suspect you're picking up heat somewhere."
    +1
  16. #12
    Apr 2018
    Gary's idea is worth a try. Fyi, Unit is producing plenty of condensate as well.
    Alternate idea would be to read the amps on the air handler in cool mode.
  17. #13
    Apr 2018
    24 hrs after removing some refrigerant, it's getting strange. DeltaT is now 14, and we changed nothing. Daily outside temp about the same as before. 14 is obviously still sub par.
    I figured maybe a possible obstruction in the lines or coils cleared itself. Maybe.
    A very sharp tech buddy says he's seen cases with R410a where adjusting a charge can take 24 hrs for the txv to adjust.???
    Never heard of such. For example, replace a compressor, drop the 410a charge and typically in 15 minutes you have stable pressures.
    Anybody heard of 24 hrs for a txv to adjust?
  18. #14
    Jan 2010
    No
  19. #15
    Apr 2020
    va
    No
    Ditto
    Valve mfg instructions list up to 15 minutes.
  20. #16
    Virginia
    Sometimes Oil gets in the wrong places and it takes a while to get back to the compressor where it belongs .... and I think it acts as a restriction
  21. #17
    Virginia
    Last week I worked on a 27 yr old Bryant 2.5 ton HP
    Found the air filter 80 percent clogged solid because someone built the trap in front of the access flap
    After about 15 minutes my SH was hanging at 30 , SC 20
    Im like .... dam ... your TXV shut down .... let me order one
    Couple days later hes like "dude its been 70 deg inside and its 95 outside"
    I havent went back yet because ive been stupid busy .... but Im guessing "oil" was messing with it
  22. #18
    Apr 2020
    va
    You had low air flow, low suction saturated, potential moisture icing at txv inlet/screen.
    Correct air flow, higher suction saturated, no icing restriction.
    Running at full load, normal conditions will return oil rapidly. Excess oil will affect discharge sh and be apparent.
  23. #19
    Jun 2022
    Central western Florida
    Amp draw to air handler will rule out electric heat stuck on. I had one the other day with a back feed through fan relay board energizing heat relay . It may sound too simple but have you tried to clean condenser coil. You know when you start hosing it out
  24. #20
    May 2018
    Santa Clarita, CA
    Bro! Me too. I had a restriction on a Bryant packaged unit. Screaming compressor, high head etc. I come back with a new txv the next morning and the Shit is purring. Didn’t understand that one til this day