Thread: True prep table evap fan direction

  1. #1
    Join Date
    Dec 2008
    Location
    NorCal
    Posts
    222
    Post Likes

    True prep table evap fan direction

    At a customer site today who has a True TPP-93D-2 serial number 1-4798463. 115v r134-a. Poor cooling and lots of condensate. Door seals ok. Unit kept closed by customer even during a rush.

    Discovered that the fan is pushing air into the evaporator. Is this design a thing for some larger prep tables?? Ive searched for an answer with no luck, but I doubt that even True would design a unit like this. (Ive only ever seen one evap with this design, and that was a 50 year old walk-in freezer.)

    I just want to be sure there isnt something about the airflow distribution into the top tray section of the cooler that Im not aware of before I tell the owner that the guy before me screwed up. Thanks.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    39,572
    Post Likes
    Yes blowing into the evaporator.

  3. Likes Bob-Brr liked this post.
  4. #3
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,147
    Post Likes
    Coldest air hits the pans first. Also look for sheet metal squares covering the round holes under the pans to restrict airflow in the pan section.

  5. Likes trippintl0 liked this post.
  6. #4
    Join Date
    Apr 2022
    Location
    Northeast US
    Posts
    196
    Post Likes
    Airflow is critical with all these prep tables, make sure that evap fan is working at full speed, I have seen several incidences where previous servicer and manufacturers accidentally installed 220v motors, These cast iron motors will also loose their "guts" when the bearings fail. Also all ducting in air stream are needed, sweat indicates low air flow!