    10 ton 3 phase Goodman R22 heat pump. No superheat, about 2 degrees subcooling on vapor side. 24-26 amps on the compressor, 30 rla. It's a bugger to get inside the unit, AND it's not even 1' away from the wall and another unit 3 feet away, maybe. so:
    Need some help here. My plan of attack, based on ease of checking:
    After checking with the manufacturer to see if its safe on this particular unit to do a draw down check the compressor. Will it draw down to 0 psig.
    Next check the reversing valve. Voltage, magnatism, smack it, check temperatures on the legs.
    Last, check the txv.
    Thoughts? Suggestions?
    Jan 2012
    Missouri, USA
    Quote Originally Posted by RedSafety View Post
    What was the indoor temps?
    Adjustable txv?
    Airflow?
    Model numbers?
    Aug 2009
    Beatrice, NE
    No SH, lo SC, all your refrigerant is stacked up in the evap. Could be a matter evap, belt slipping, motor running backwards, supply damper closed or return also. Possible metered g device over feeding.
  4. Likes R600a, Red850kid liked this post.
  5. #4
    Apr 2020
    va
    Complete readings or just a big hammer?
  6. #5
    Apr 2022
    Springfield, MO
    Indoor temps, about 74 DB.
    Adjustable txv? Can't see it well enough to tell.
    Airflow? Delta T just under 17 degees. Cooling well, but sight glass is gassed over.
    Model number GSH101203AD
    It does cool well, interestingly. Only checked it because I was trying to find out why the other unit blew a fuse. Someone else checked that one and only replaced the breaker, but didn't try to find out why it blew. Low charge and almost totally felted over and frozen coil. While I'm up on the platform, might as well check the other unit, right? Been years since it was serviced. And despite being a heat pump, no insulation on the liquid line! But no worries, converted to hot water heater.
  7. #6
    Mar 2013
    East Concord, NY
    Why would it? It's never done in my area.
    Nest is POO!!
  8. Likes R600a liked this post.
  9. #7
    Cincinnati, Oh
    Low airflow and low charge.
  10. #8
    Apr 2022
    Springfield, MO
    Low charge? Because the SC is low? Then why is the SH also low? I added 2 lbs that I shouldn't have added because I thought the same thing initially, but zero change in SC and SH.
  11. #9
    Apr 2022
    Springfield, MO
    Quote Originally Posted by HVAC_Marc View Post
    Maybe because the installation manual specifically says it must be insulated? The TXV is outside on a heat pump, not indoors. Big temperature drop on the liquid line without the insulation.
  12. #10
    May 2014
    Bay Area California
    I do not understand the highlighted statement.
    I do a triple evac with nitro to remove non condensables.
    I'm feelin' a little peculiar.
  13. Likes R600a, vin lashon liked this post.
  14. #11
    Apr 2022
    Springfield, MO
    Quote Originally Posted by BBeerme View Post
    In other words, -2 degrees of superheat.
  15. #12
    Mar 2013
    East Concord, NY
    I just re-read my Lennox heat pump installation manual. Nothing in there about LL insulation. Perhaps your OEM is different. In my case it doesnt matter much as it all runs through conditioned space.
    Nest is POO!!
  16. Likes R600a, pacnw liked this post.
  17. #13
    May 2014
    Bay Area California
    That would mean liquid refrigerant is entering the compressor. I would suspect one of your instruments or other is well out of calibration
  18. Likes R600a liked this post.
  19. #14
    Mar 2015
    Medford, N.Y.
    Air temps indoor/outdoor/IDWB?press's/crazy dirty/plugged evap/blower wheel/ txv thermal bulb strap loose/broken/missing?Full SG?
  20. Likes R600a liked this post.
  21. #15
    Apr 2022
    Springfield, MO
    Yup, most likely.
    If the gauges were off, then the numbers would be off for all the other units I've checked, but they are not. The other unit next to it clearly shows low charge, 15 degrees SH, 7 degrees SC, and expected pressures.
  22. #16
    Apr 2020
    va
    Yup, most likely.
    Then you have a pump & not a compressor.
  23. #17
    Aug 2009
    Beatrice, NE
    Yup, most likely.
    How do you figure, your temp probes could be off by 2 degree and you would be looking at 0 SH on the unit in question and 17 SH on the other one and the other one would still be considered in normal range.
    The only way you know if your test equipment is good is either run a calibration test on it directly or do a comparison with a "known good" test instrument.
    When readings don't make sense you have to test the test instruments.
  24. #18
    May 2014
    Bay Area California
    What you told us is that you have negative superheat. And just for the record, in a "common normal" system, that is not possible.
    Yup, most likely.
  25. Likes HVAC_Marc liked this post.
  26. #19
    Mar 2015
    Medford, N.Y.
    Yup, most likely.
    What does "expected pressures" mean? Provide the actual press readings and let us decide if they are "normal" or not.
  27. Likes R600a, BBeerme liked this post.
  28. #20
    Apr 2022
    Springfield, MO
    Quote Originally Posted by BNME8EZ View Post
    75.0 to 75.2 degrees across 4 different thermometers. Virgin tank of R410A in the same room, 218.1 PSIG. Looks good to me.