    York YVAA0345 condenser fans

    Hey fellas , Working on a YVAA and notice that Cir B was tripping on HPCO. I found all ( 9 ) 30 amp fuses blown . We replaced all 9 bus fuses and I was thinking good to go. Well the ABB drive for the condenser fans never came to life , not getting the voltage to the ABB drive to control the fans.

    I know that the drive will not power until the compressor sends the signal .

    I am returning to the site tomorrow for more investigation, the call came in at 2pm .

    Not sure what I should really be looking at , the trigger board , diode module , IGBT or the VSD logic board .

    Your thoughts ?

    Thanks
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  2. #2
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    670
    Post Likes
    I would suggest to look at fan contactors and fan motor.
    If I remember right there is a contactor before the vfd.

    Trigger board, logic board and IGBT is for the compressor only

  3. #3
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes
    Thread Starter
    I saw the contactors, I will double check them today, it seems that the contactors are not pulling in - what calls for the contactors to pull in ? I feel that what calls for the contactors is the issue.

  4. #4
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Is this the correct wiring diagram
    Attached Thumbnails Attached Thumbnails Screenshot_20220722-065046~2.png  

  5. Likes Red850kid liked this post.
  6. #5
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by milkyway View Post
    I saw the contactors, I will double check them today, it seems that the contactors are not pulling in - what calls for the contactors to pull in ? I feel that what calls for the contactors is the issue.
    the chiller microboard calls for the contactors to pull in and feed the drive. power issues can cause the fuses to fail but so can bad wiring and a bad drive. take your time and investigate properly.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  7. #6
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes
    Thread Starter
    Got it - bad drive .Thanks everyone

  8. Likes VTP99 liked this post.
  9. #7
    Join Date
    Jul 2015
    Location
    Ireland
    Posts
    665
    Post Likes
    Have you tried going into service mode and powering the drive from there?

  10. #8
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    Quote Originally Posted by milkyway View Post
    Got it - bad drive .Thanks everyone
    No - not yet . Use the service mode call for fan contactors and then send it a speed signal.
    Check all fan motors and the wiring cables going out thru the chiller housing.
    If the drive has failed there are plugs in the drive enclosure to by- pass the drive until it can be replaced.


    Sent from my iPhone using Tapatalk

  11. #9
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes
    Thread Starter
    After looking at circuit 1 condenser fan drive set up and following the wiring up to the control cabinet where the contractors are I discovered that I made the mistake of checking for voltage at the fuses in the ABB drive cabinet rather than the incoming power to the drive itself.
    I have 480 to the drive and nothing powers up. After looking closer I seen where there had been an electrical failure on the back side of the board.


    I never went into service mode and sent a speed signal to the fans.
    I will have to keep that in mind for the future.
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •