    I check every wire inside the condensor in a situation like that, even as sop when doing a call. have seen where passed through wall or floor where wires were cut against duct or lineset. sometimes wire use between in and out are switched so dead end strands wrapped around tstat wire may be energized and rub on one of panels and short
    Col 3:23


    questions asked, answers received, ignorance abated

  2. #22
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    went there today to go over the whole OD unit .... nothing wrong

    It was running when i got there

    I have a Short Pro Tool on it .... and somehow it stays running
    Tell your Cat I said "Psst Psst Psst"

    It seems like everywhere I go the AC is broken

  3. Likes R600a liked this post.
  4. #23
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    went there today to go over the whole OD unit .... nothing wrong

    It was running when i got there

    I have a Short Pro Tool on it .... and somehow it stays running
    I can send you one with 1/4" spade terminals on it so that you can just plug it in permanently.
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  5. Likes Snapperhead liked this post.
  6. #24
    Join Date
    Mar 2013
    Location
    East Concord, NY
    Posts
    22,646
    Post Likes
    the simple fix is to bypass the fuse and look for what burns (or use a thermal camera).
    Nest is POO!!

  7. Likes Snapperhead liked this post.
  8. #25
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    Throw a time delay resettable fuse on the source, install multiple 3 amps fuses at each load. The one that blows is your problem

    Sent from my SM-N960U using Tapatalk
    ...

  9. #26
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    So you think a 5 amp time delay .....ok time to Google that
    Tell your Cat I said "Psst Psst Psst"

    It seems like everywhere I go the AC is broken

  10. #27
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    "How To Properly Diagnose Low-Voltage Short Circuits in The Field" an article in "the NEWS" the weekly newspaper, in the March,19,2018 issue.

  11. #28
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    So you think a 5 amp time delay .....ok time to Google that
    Well the transformer is toast long enough at 3 amps.. in all likelihood and hopefully the short is quick. I use a 5 amp time delay. It takes 3-5 sec to trip which is certainly long enough for a fast blow to trip first

    Sent from my SM-N960U using Tapatalk
    ...

  12. #29
    Hurst11 is offline Professional Member/Membership Committee
    Join Date
    May 2020
    Location
    Haskell Oklahoma
    Posts
    1,529
    Post Likes
    2 summers ago I fought one for a week that would sometimes run for 5mins then pop fuse or it may run for a day and a half. It was so random and could not find the short. I just gave up after the 3rd time I was there and ran a temp stat wire outside to the pump from the air handler inside, down the hallway out the garage door and hooked it up and told the lady to call me when it quits working. She called a week later and said there has been no more problems. Re ran stat wire and all good since.
    I checked the wire multiple time visually and with my meter, I prolly coulda found it quicker if I had a megger back then.
    Sometimes ya gotta throw something at the wall and see what sticks.

  13. Likes R600a, Snapperhead liked this post.
  14. #30
    Join Date
    Nov 2018
    Location
    Western Maryland
    Posts
    214
    Post Likes
    Seen many a discharge lines with wires laying on them and eventually they will melt and trip. System shuts down and all gets cooled down and no problem until those long run cycles kick back in nd things heat back up...I've seen it more than once

  15. #31
    Join Date
    Sep 2018
    Location
    Summerville SC
    Posts
    112
    Post Likes
    Look for chewed wiring or something laying on a pipe

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •