  1. #21
    R600a's Avatar
    R600a is online now Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    19,475
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    Did you see a little round glass ... like in the copper piping in compressor area

    Thats for watching the freon go by ...
    I like that. I might add it to my signature.
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.

  2. Likes Snapperhead liked this post.
  3. #22
    Join Date
    Jun 2022
    Posts
    5
    Post Likes
    Thread Starter
    No glass window.

    This unit is cooling a freezer set to -3. When it reaches temp at the end of each cooling cycle the compressor turns off. Then after a few seconds it flips back on again for about a second and turns off and then sometimes does it once more. For the entire 2 years I have owned it I have lived with this 1 to 2 short cycles. For the last couple weeks though it has gotten progressively worse, sometimes cycling on and off over a dozen times in quick succession. I'll be calling every refrigeration guy in town tomorrow to see if there is someone left in this city that is willing to do honest work at a fair price despite the fact that my desperate situation makes me ripe for extortion.

  4. #23
    R600a's Avatar
    R600a is online now Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    19,475
    Post Likes
    Quote Originally Posted by ryantomaz View Post
    No glass window.

    This unit is cooling a freezer set to -3. When it reaches temp at the end of each cooling cycle the compressor turns off. Then after a few seconds it flips back on again for about a second and turns off and then sometimes does it once more. For the entire 2 years I have owned it I have lived with this 1 to 2 short cycles. For the last couple weeks though it has gotten progressively worse, sometimes cycling on and off over a dozen times in quick succession. I'll be calling every refrigeration guy in town tomorrow to see if there is someone left in this city that is willing to do honest work at a fair price despite the fact that my desperate situation makes me ripe for extortion.
    Have you checked the contractor locator map on this site?
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.

  5. #24
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    11,303
    Post Likes
    Quote Originally Posted by ryantomaz View Post
    No glass window.

    This unit is cooling a freezer set to -3. When it reaches temp at the end of each cooling cycle the compressor turns off. Then after a few seconds it flips back on again for about a second and turns off and then sometimes does it once more. For the entire 2 years I have owned it I have lived with this 1 to 2 short cycles. For the last couple weeks though it has gotten progressively worse.
    Uhh hello ... Did you look at post number 13 ? ?
    Tell your Cat I said "Psst Psst Psst"

  6. #25
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    11,303
    Post Likes
    Quote Originally Posted by ryantomaz View Post

    This unit is cooling a freezer set to -3
    This is why the installer put in R404

    Im thinking you don't need to change Refrigerants
    Tell your Cat I said "Psst Psst Psst"

  7. #26
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    9,947
    Post Likes
    OP, post #6 & #15 both mention that burnt yellow wire.

    Short cycling of the comp does damage the comp. The windings inside the comp "flex" and move and rub against each other, possibly leading to a shorted (dead) comp.

    Why would an evacuation process need to be done?

    Is that timer in the photo set for 240 seconds ?

    How does a delay on make timer cause a problem ,other than maybe a very slight temp rise of the box?
    Last edited by TechmanTerry; 06-23-2022 at 05:11 AM.

  8. #27
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    38,793
    Post Likes
    The kicker here is that I am actually only 2 years into a 4 year warranty from Russell. I have already brought this issue to their attention and they say it only covers the cost of a new unit

    Russell isn't going to warranty anything except defects in material and workmanship on there end, all your issues is caused by the installing contractor. Refrigerant leaks are not covered by the factory.

    You need to find a contractor that knows what there doing.

  9. #28
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    11,303
    Post Likes
    I dont think it has a leak ....

    How did the last guy determine it has a leak .... when .... the Box pulls down to -3 .... and ... there isnt even a SG to look at

    He didnt mention the Non English speaking Tech - torching the receiver either

    P.S. ... the next time someone shows up who cant speak english , send him packing lol , those guys mess up more crap than they fix !
    Tell your Cat I said "Psst Psst Psst"

  10. #29
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    11,303
    Post Likes
    Ryan ... hook up the Delay for heavens sake
    Tell your Cat I said "Psst Psst Psst"

  11. #30
    Join Date
    Jan 2021
    Location
    Lynchburg, VA
    Posts
    16
    Post Likes
    Quote Originally Posted by ryantomaz View Post
    Thank you Restaurant mech! You have provided much needed perspective. For the last 2 years I have constantly stressed about the 1-2 short cycles but as you suggest that might not be a huge problem by itself.

    Of course as of late it has begun short cycling upwards of a dozen times in quick succession which suggests that something has begun to slip.

    I believe the suction line is well insulated.

    Would the fact that this unit wasn't vacuumed prior to being charged up be a potential contributing factor?

    Assuming a professional will be servicing this unit asap would it not be preferable to use the time delay to prevent hundreds of unnecessary startups each day in the mean time?
    If you want to kill the compressor it will be a excellent idea.

    Sent from my SM-N975U using Tapatalk

  12. #31
    Join Date
    Jan 2010
    Posts
    31,657
    Post Likes
    If it's a scroll there's a good chance the discharge check valve is bypassing.
    There was just another thread on this and I had one last week.
    On shut off the high side will leak to the low and cause rapid short cycling of off then on.

  13. Likes Snapperhead liked this post.
  14. #32
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    11,303
    Post Likes
    Quote Originally Posted by droopylee95 View Post
    If you want to kill the compressor it will be a excellent idea.
    Can you go into detail exactly how this will happen .... because I dont agree ... like at all

    Take a good look at the Delay he has https://www.icmcontrols.com/product/icm203/ its whole purpose is for Short Cycling

    He should hook up that delay until a Professional comes out

    This will buy him a few days until that happens
    Last edited by Snapperhead; 06-23-2022 at 07:52 AM.
    Tell your Cat I said "Psst Psst Psst"

  15. #33
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,615
    Post Likes
    Its also very likely due to it being summer time that the DTC valve to keep compressor cool is continuing to feed some refrigerant from liquid line back into compressor shell, which adds to the short cycling. A lot of mfg's dont use a solenoid on the liquid injector valve because "once compressor shuts off the valve should cool off and stop injecting." Which sounds great, but reality is every summer we see units short cycling from this.

    Sent from my SM-G892A using Tapatalk

  16. Likes Snapperhead liked this post.
  17. #34
    Join Date
    Aug 2019
    Posts
    83
    Post Likes
    If the compressor is shortcycling on temp, then you have either a bad compressor with bad suction valves or a leaky liquid line solenoid. ***************

    DIY assistance is not allowed in the "OPEN" forums. Your comment on rewiring the TDR have been removed.