So I just finished piping in a walk in freezer, when I went to add nitro into my liquid line my suction side comes up to about 60-65PSI and stops while my liquid side gets to the 150PSI I have my reg set to. I tried waiting to see if it would eventually equalize but it doesn’t. I tried holding the sensing bulb in my hand but it does nothing. If I open the TX up from the adjustment I get flow. I heated the bulb with a lighter and it took some time to start flowing. So I also tried replacing the power head and it does the same thing, although it did open much quicker when I put my lighter to it. My solenoid is open with a mag. The TXV is an SSE-6. The evap and components are out of an old freezer that was running but was required to be relocated. So it was working. Any help or advise would be much appreciated.
Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
Posts
31,874
Post Likes
Likes (Given)
51116
Likes (Received)
14502
Dislikes (Given)
0
Dislikes (Received)
25
Is it a MOP pressure limiting TXV?