Originally Posted by
VGA
I would start by explaining to the client why there are 2 pumps, that in his sys there are 2 separate chill wtr flows reqd, 1st being the primary pump supplying the wtr flow reqd for the chlr evap and then there is the 2nd pump/ secondary loop which meets his process tool wtr flow req protected by ( a preset internal flow switch tied to the tool control voltage) and the heat rejection req before being ret back to the tank as warm wtr.
If this original design is changed then a temp controlled modulating 3 way control valve could be installed before ch wtr enters the tool which will divert the unneeded chill water back to the open air tank. This wld also lower the temp of the water in the tank, lowering the load on the process chiller as unused very cold water is being ret into the tank.