+ Reply to Thread
Results 1 to 20 of 23
Thread: VAV Air balancing
    May 2022
    VAV Air balancing
    Hi
    I am new to hvac world.
    I want to know about air balancing in VAV system.
    I mean what is the process and how to accomplish it.
    If any one having documents about it please share.
    Also what is diversity VAV system ?
    Sorry if this post seems vague, I didn't want to get to wordy.
    May 2009
    Quote Originally Posted by DMHBMS View Post
    Hi
    Contact these organizations for educational information.......
    https://nebb.org/
    https://www.aabc.com/
    This is an extremely simplified explanation, .........DIVERSITY in a system is the intentional under sizing of the mechanical equipment....basically, with the intent to save energy and operating cost........
    WAYNE.........where are you.....?
    Feb 2016
    Louisburg Kansas
    Artrose You gave him as good advice as I can. There is too much to cover to advise him in this thread as to how balance should be done on a VAV system. He has to calibrate the VAV's and how to do that depends on the equipment he has and the control program.
    He also needs to know how the diversity is intended to work. An example is that in some portions of the building at a given time during the day the airflow needed to maintain temperature set point will be less than others.
    NEBB is a good place to get the information he needs.
    Thomas Jefferson
  4. Likes dieseldude, Allen liked this post.
  5. #4
    May 2014
    Bay Area California
    I do a lot work on this stuff.
    In a nut shell, here's how it goes . . .
    On a small system like an Intellipak, there is no balancing. Volume controllers have been tweaked to be entirely useless.
    On a multi-story building, especially with one LARGE blower, balancing is critical. You need prints to get it right.
    I do a triple evac with nitro to remove non condensables.
  6. #5
    May 2009
    Quote Originally Posted by BBeerme View Post
    Please explain what you're talking about with that Intellipak........?? No balancing...?? What are volume controllers...??
  7. #6
    May 2014
    Bay Area California
    If all you are doing is resi work, then not worth the time to go into.
    There's no VAV's in resi.
    Quote Originally Posted by Artrose View Post
  8. #7
    New Mexico
    Unless specified many systems call for 80% of the VAV's to be open when adjusting the air handler. The idea is that at any one time some will be closed. Once that's done the process is to balance the trunk lines. Was that what you asked. What powers your boxes?
    Tech stuff on the brand of the boxes can be found on the net.
    We are here on Earth to fart around ......Kurt Vonnegut
    You can be anything you want......As long as you don't suck at it.
    USAF 98 Bomb Wing 1960-66 SMW Lu49
  9. #8
    May 2009
    Quote Originally Posted by hvacker View Post
    The 80% comment is bogus......In a pressure independent system, it is only necessary to have sufficient pressure in the main supply duct to satisfy the needs of the box, or group of boxes that you are balancing......
    To balance the airflow on series fan powered vav boxes, it's not really necessary to satisfactorily balance these boxes with any airflow from the air handler.....
    After the series fan style of box is balanced, you set the box pressure to neutral or slightly negative......
    Once you have completed any vav system box balancing, then is when you drive the entire system to max cool and do your traverse.
    Any need for sheave changes is then determined.
  10. #9
    May 2009
    Sorry, there are also variable volume systems in residential too......
    Maybe not the traditional vav's we have in commercial, but vav none the less.....
  11. #10
    Feb 2016
    Louisburg Kansas
    The first thing I did was drive all the boxes to full cool because I wanted to traverse the main duct first. If low on airflow I drove the freg drive to where ever needed above 60 hz to determine if the AHU was capable of delivering air at design. It is also easy to determine sheave sizes required to obtain the needed AHU speed at 60 Hz. On systems with diversity I always set the AHU airflow about 10% above design (which is acceptable) in case the engineers design wouldn't do the job.
    In a VAV system with diversity all boxes are balanced to max design airflow. The cooling load determines the airflow required to cool each space. Traditionally in the morning the east boxes will be at full cool if the temperature requires for cooling and the west boxes will not be at full cool. In the evening this will reverse. In short you don't balance for diversity the controlls take care of it if working properly and balance is correct.
    All VAV'S and FPB'S have to have the calibration checked. You need to study how to balance and calibrate prior to starting.
    Thomas Jefferson
  12. Likes ksefan liked this post.
  13. #11
    May 2009
    Quote Originally Posted by WAYNE3298 View Post
    Good point Wayne......Doing the preliminary traverse is a very good idea because it gives you a good idea where you stand from the get go......If you have the time....
    And yes, all boxes need to be checked for proper operation, mechanical condition, flo tubes correct, rotation correct, stroke times correct, software programming correct, etc., etc........
    And most certainly with DDC, they must have undergone a start up procedure, in which the box goes through it's calibration period.....
    Thing is, when it's very hot, those unbalanced boxes will drive to wherever they think they need to be, and depending on time and money, it's only necessary to manually close enough boxes to achieve enough main duct supply pressure to satisfy what you're working on.......(in general)
    Without that preliminary traverse, as you proceed forward with your balancing, and you start to bring more and more boxes under control, you begin to know where you stand with respect to available duct pressure.......
    I'd still like to know....... Please explain what you're talking about with that Intellipak........?? No balancing...?? What are volume controllers...??
  14. #12
    May 2014
    Bay Area California
    Now my head hurts.
  15. #13
    May 2009
    Now my head hurts.
    Come on now BB...this is a place of learning isn't it..??
    We need to pass on accurate information, and unfortunately a lot of this stuff is not easily learned from books, or by simply talking about it......
    Much of this requires hands on with a mentor guiding you......
    I apologize for jumping so hard sometimes, but when incorrect, or inaccurate information is passed, I have a hard time letting it go........
  16. Likes WAYNE3298 liked this post.
  17. #14
    Feb 2016
    Louisburg Kansas
    [QUOTE] We need to pass on accurate information, and unfortunately a lot of this stuff is not easily learned from books, or by simply talking about it......
    You are dead on Artrose. I have seen experienced air balance guys stumped when the VAV'S wouldn't calibrate.
    Of course BBeerme likes to have a little fun.
    Thomas Jefferson
  18. #15
    May 2014
    Bay Area California
    I was actually very serious in what I said.
  19. #16
    New Mexico
    Opening the boxes is the first step in most systems. The 80% I wrote was like said, Unless specified.
    T&B is all about procedure. If procedure isn't followed it will result in more time and needing to wrestle a system.\
    into compliance.
    The beginning of a T&B is 1st do the paper work. In a constant volume system, all the outlets are opened.
    2nd adjust the air handler to spec. SP, amps, rpm, and all that applies to the fans. Do a traverse.
    In one case the spec asked for 1/2 plugged filters. This was done with cardboard.
    Different systems can require adjusting methods but usually not al that different. If specs call for 80% open before doing a traverse or wide open would depend on the engineer. Like said the idea is to save some energy by not needing a fan to be adjusted full bore when all the boxes won't be full open.
    A system has to be adjusted to spec before boxes can be adjusted.
    This is what I learned from SMACNA when I got certified.
  20. #17
    May 2009
    into compliance.
    Correct....after you have been selected to do the balance job......before the install is complete, walk the job, visit the subs, prep your paperwork, spot check the finished installation, do your preliminaries, then begin your balance work......
    In a perfect world, with a constant volume, or a variable volume air system you must be certain that all dampers in the system are wide open, and if there are any splitters, etc., these devices should also be adjusted to allow for free flow of air in the system.
    A spot check of the system is also in order to determine if there are any obvious deficiencies. We find all kinds of issues, wiring, flow tubes crossed, off, pookie, missing, loose insulation, flex blown off, shipping cardboard left inside air handler discharges, incorrect programming, on and on...
    One of the best finds were the parallel fpb's that were hung inverted. Barometric dampers won't close when gravity is on their side.......Water systems are not immune either....coils piped incorrectly, plugged strainers, on and on...
    The ahu filters must be clean, and it's preferable to work with a system that has been running and stabilized ...if possible.......
    If you are carrying around a cert, then you know that there are several different designs of vav terminal boxes.....You also know the different methods necessary to balance the different designs.
    It is preferable to adjust your ahu to as close to design as possible before you start balancing boxes, but it is definitely not required before you can balance vav's......
    Yes, occasionally an engineer, or a building owner might ask for something special, or out of the ordinary, but that is rare......
    I've seen all kinds of T&B folks out there......some really good, some lost, and I watched one group escorted off the jobsite........
    As a T&B tech, I've balanced thousands of vav's, and as a Control man I've set up, programmed, and serviced thousands more..... Today, amongst the other things that I do in this career field, I teach this crap......
    You do what you got to do.......
  21. #18
    May 2014
    Bay Area California
    Used to be virtually all VAV systems were pneumatic. Volume controllers are the device where you set the minimum and maximum air flows. A conditioned space served by an Intelipak is rather small, relatively speaking, compared to a multi story building. And I have NEVER seen one of those spaces where most if not all of those volume controllers were either never set proper or techs have tweaked them through the years to go full open and full closed. Those systems work just fine. Mainly because the Intellipak was sized to operate with all VAV's fully open.
    On multi story buildings, balancing is critical, as the equipment is not sized (as mentioned earlier) for the whole building all at once due to the varying heat loads due to the way the sun moves.
    I can tell a story from decades ago. Picked up an account with a few 6-8 story buildings. This one building had multiple complaints from the tenants. They said problems for years. Co-worker went to troubleshoot. Probably spent a couple of days trying to figure out the problems. Since the entire building was having problems, he went straight to the roof top equipment. He finally called the boss, and boss dude sent me in.
    Co-workers biggest complaint was very low temp split. This is a huge evap with a 100 hp or larger blower motor. He said everything checks out on the refrigeration side. Typically on these types of problems I tell the tech to stop, let me do my discovery without other input. These air handler rooms are large enough for 20 homeless to easily live in. I take a quick look around. Check some basics like superheats and amp draws. While checking superheats, the air is really moving, blower pretty well maxed out on amps.
    Let's go down to the trucks. I tell him I think there is too much air flow, likely the building needs to be balanced, grab your ladder.
    Pop the first tiles and find the VAV. Volume controller was removed. So I explain what a volume controller is and why it is in the system. You need minimum air flow to get fresh air, and the max air flow is how you meet the engineering design specs. It ended up that EVERY SINGLE volume controller had been removed. It was very expensive for the building owners to correct.
    We did one floor at a time. Couldn't even properly balance because the supply air pressure was too low. So we just randomly set them so the VAV's would not fully open. After we were done with that, the air pressure went way up. Tenants were thanking us, said it felt so much better, and that was befre balancing. Then we went floor by floor doing the balancing. Very time consuming, which means very expensive to the customer.
  22. Likes ksefan liked this post.
  23. #19
    Feb 2016
    Louisburg Kansas
    I've seen some bad situations BBeerme but nothing screwed up that way. It had to take forever to get the air balance completed. Good job!!
    Thomas Jefferson
  24. #20
    May 2014
    Bay Area California
    Fortunately, they still had the original prints with specs. We kept telling the tenants there may be some discomfort while we do this, and we're going to make a mess (ceiling tile debris), and this is going to take awhile because we are working throughout the entire building.
    Tenants were SO happy, just with installing the volume controllers, they would say it already feels so much better.
    If I remember correctly, like with installing the new volume controllers, I just spent one day there doing the first floor. Showing my co-worker exactly what to do, and no more. Then they sent in another helper, mainly for popping tiles and locating the VAV's.
    Then for the air balance, again, I just did the first floor, showing my co-worker the process. Sort of a two step process. First go through and open all manual dampers and set the min max on the volume controllers. After that was done on all floors, you get the balance cone and adjust air flow to the registers via the manual dampers; again, I just did the first floor showing my co-worker the way I do things. Then another helper was sent in.
    We got praise after praise from the tenants. Just walking the halls or in the elevator.
+ Reply to Thread
Quick Reply Quick Reply
Register Now
Log-in
  • You may post new threads
  • You may post replies