    Frigidaire heat pump issues

    I'm working on a frigidaire heat pump. I had a restriction and changed the txv and drier and flushed and added new gas. It ran for a couple of weeks and now I'm pumping down and have 1 degree sub cool and sky high super heat. When I go to heat liquid pegs to 600 and suction is good. I'm missing something I just don't know what. I have good air flow. Indoor coil is micro channel if that matters.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Pull and weigh the charge.

  3. #3
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    What is the outdoor metering device ?

  4. #4
    Join Date
    Apr 2022
    Posts
    3
    Post Likes
    Thread Starter
    Txv

  5. #5
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Which txv did you replace ?

  6. #6
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Which type of filter drier did you use ?

  7. #7
    Join Date
    Apr 2022
    Posts
    3
    Post Likes
    Thread Starter
    Only has txv in air handler and I replaced it with oem. Used a biflow filter, and the condenser has a piston

  8. #8
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Have you tried warming the TXV power element bulb ?

  9. #9
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Is there a bypass around the txv with a check? Did you pull the orifice when it was open?

  10. #10
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    What is the temperature or even better, the pressure drop across the filter drier?



    Sent from my SM-G965W using Tapatalk

  11. #11
    Join Date
    Feb 2004
    Location
    tenn
    Posts
    397
    Post Likes
    is it original a coil had several nordyne micro channels given to me warranty and shoulds have been copper and tubes
    birdman

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •