Thread: Kolpak Arctic Fox Evaporator Coil and KE2 Controller

  1. #1
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes

    Kolpak Arctic Fox Evaporator Coil and KE2 Controller

    Anyone have any experience with this setup? I am trying to diagnose whether or not I have a bad Electronic Expansion Valve (EEV) or an issue with the KE2 controller on this walk-in-cooler. I'm getting a HSH (High Superheat) alarm.

    I put my eyes on this particular setup for the first time yesterday and it's kicking my a**. After doing some research, I understand what all the components (KE2 controller, KE2 remote display, electronic expansion valve, temperature sensors and and transducer) do, but before I call technical support, I'm trying to get all my ducks in a row so I don't sound like an idiot when I describe what's going on with this system.

    I haven't checked resistance across the EEV leads yet, but I plan on doing that tomorrow. Also, I plan on manually operating the valve to check that it's operating properly.

    FYI, this system was installed by "others" and it's been running without any obvious issues for 2-1/2 years, but I wouldn't be surprised if I have a restriction at the EEV (trash, moisture, oil, etc.) based on the issues the system is exhibiting. Thanks!

    https://ke2therm.com/product/ke2-evap-oem/
    https://ke2therm.com/wp-content/uplo...ember-2018.pdf
    With your chrome heart shining in the sun, long may you run.

  2. #2
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    First... what you working on man?
    Walk in obviously, but prep room, storage, meat, etc?

    How many evaporators? 1 condensing unit?
    Brand of condensing unit?

    Is there a liquid solenoid on this or just the EXV?
    Where I would start, would be to confirm that the KE2 controller is seeing the correct info. If either the transducer or the suction line temp sensor are incorrect then there is no way the EXV will modulate correctly.
    Watch the system operate while you are tapped on and monitoring actual pressures, temps, and superheat and see what these readings compare to the what the controller is seeing.
    Make sure you have a clear sight glass and no temp drop across your liquid driers.

    Sent from my SM-G975U using Tapatalk

  3. Likes VTP99 liked this post.
  4. #3
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    It’s a medium temp kitchen walk-in-cooler at an elementary school.

    One 2-fan evaporator coil with EC motors.

    Pump down R-438A system on a Kolpak condensing unit with high/low auto-reset pressure controls, Sporlan head pressure control valve, drier, receiver, typical stuff for a walk-in-cooler.

    I don’t know what the controller is seeing. It was never given internet access, so I can’t access the web page with sensor and other data.
    With your chrome heart shining in the sun, long may you run.

  5. Likes UmmScott liked this post.
  6. #4
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    You should be able to get into that controller relatively easily.
    Most KE2 controllers you hold down the left and right buttons for a short bit to access a quick menu which shows most inputs.

    If its locked, you'll have to gain access to it somehow and will need to contact KE2. Their tech support is pretty good..

    If you get the system to run, you could unplug the EXV while you observe. ExVs are stepper motors and dont move unless they're called to. So if you remove power, they stay where they're at until they're commanded again by the controller

    Sent from my SM-G975U using Tapatalk

  7. Likes SandShark liked this post.
  8. #5
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    .
    Attached Images Attached Images  

  9. Likes SandShark, UmmScott, Turtleman liked this post.
  10. #6
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    .
    Yeah, it’s the link in my first post. Thanks.
    With your chrome heart shining in the sun, long may you run.

  11. #7
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Is the condensing unit running?

  12. #8
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    If you want access from a lap top you would only need a Ethernet cable

  13. #9
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    Name:  5768ACC7-1375-4B85-BDA4-0BA5B369B7C9.jpg
Views: 712
Size:  153.6 KB
    Quote Originally Posted by itsiceman View Post
    Is the condensing unit running?
    Yeah, it runs as long as the EEV is feeding the coil. Several times, the valve has stop feeding and causes the condensing unit to pump down and cycle off on low pressure.

    Does this look like it’s been overheating?
    With your chrome heart shining in the sun, long may you run.

  14. #10
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Doesn't look good from here.
    Can you determine where the burning has come from ?
    How the valve body look ?

  15. #11
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    Doesn't look good from here.
    Can you determine where the burning has come from ?
    How the valve body look ?
    Name:  CFA1D179-6FA7-4309-BCCA-59D759CD8178.jpeg
Views: 700
Size:  1.83 MB
    With your chrome heart shining in the sun, long may you run.

  16. #12
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    The whole kit (valve body, stepper motor with wiring harness) on order next day air early AM. FYI, suction line temperature, suction pressure and resulting superheat were on point when the EEV was feeding properly, but then things would quickly deteriorate once the EEV became erratic. One minute it was feeding and throttling, the next minute it would stop feeding altogether, resulting in pump down.
    With your chrome heart shining in the sun, long may you run.

  17. Likes VTP99 liked this post.
  18. #13
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    LLSV looks new I wonder if they hit that stepper with the torch when installing it ?

  19. #14
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    Hopefully, they didn’t have it on the valve when they were brazing! 😬 But, you never know, right?

    Thanks for the help!
    With your chrome heart shining in the sun, long may you run.

  20. #15
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    I'm thinking they did how else would that burn mark get there unless it's an internal short ?

  21. #16
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    The million dollar question.
    With your chrome heart shining in the sun, long may you run.

  22. #17
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    That valves been overheated!


    Stay Brite #8 is your friend!

  23. #18
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Ever get into the control and see if gas is set right or other measurements?

  24. #19
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Thread Starter
    Quote Originally Posted by itsiceman View Post
    Ever get into the control and see if gas is set right or other measurements?
    Yes, I did check which refrigerant and it was set for R-448A and the right stepper motor. All other parameters were set correctly.

    I am happy to report that a new valve and stepper motor were installed today. Cooler is running and cycling on/off. The only question unanswered is what caused the stepper motor to burn up?

    For comparison, here are photos of the old and new stepper motor.

    Name:  IMG_7325.jpg
Views: 645
Size:  171.7 KB

    Name:  IMG_7327.jpg
Views: 671
Size:  121.2 KB
    With your chrome heart shining in the sun, long may you run.

  25. #20
    Join Date
    Apr 2013
    Location
    SE Nebraska
    Posts
    391
    Post Likes
    I believe that you don't want to use a solenoid on systems with an EEV. Pretty sure the KE2 will close the stepper and that acts as your pump down. This has nothing to do with the motor failing, just an FYI. It does look like overheating may have burned off the coil windings varnish and it shorted. Did you measure the resistances between the windings/case?

  26. Likes UmmScott liked this post.
+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •