Thread: noodle scratcher...randomly overcooling walk in cooler

  1. #21
    Join Date
    Mar 2022
    Posts
    11
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    I would change your Anti Short Cycle to 5 minuets.

    Cut in at 40 with a 5° differential
    update - I chatted with Emerson and they said replace the controllers. not what i was expecting from the mfg. the support person suggested that it could be amp draw from the compressor and that the settings in the controller can affect the contacts ?!?!!?

    ill try changing the antishort from 1 to 5.

    any other theories and ways to find whats causing the random 60 minute overcool is so appreciated!

  2. #22
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    The control is only wired to the solinoid correct ?

  3. #23
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Quote Originally Posted by PharmaPhridge View Post
    update - I chatted with Emerson and they said replace the controllers. not what i was expecting from the mfg. the support person suggested that it could be amp draw from the compressor and that the settings in the controller can affect the contacts ?!?!!?

    ill try changing the antishort from 1 to 5.

    any other theories and ways to find whats causing the random 60 minute overcool is so appreciated!
    Tell the Support person hes full of $hit!

    the controller closes the EEV or solenoid valve and the compressor pumps down.

  4. #24
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Unless he's got the controller wired to the contactor 😲

  5. Likes R600a liked this post.
  6. #25
    Join Date
    Mar 2022
    Posts
    11
    Post Likes
    Thread Starter
    i agree the support person was not helpful. the controllers are wired to the solenoids. the low pressure switches are wired to the contactors. (rem two independent units).

  7. #26
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Doesn't the Keeprite evap MN# start w/ the letter K, like KLV ? Are the evaps facing/blowing into each other?

  8. #27
    Join Date
    Mar 2022
    Posts
    11
    Post Likes
    Thread Starter
    good question..two keeprite units are installed in the ceiling and opposing each other about 12 ft apart. however they are never running at the same time and are completely independent of each other.

  9. #28
    Join Date
    Mar 2022
    Posts
    11
    Post Likes
    Thread Starter
    thanks a million PECSMG! since i updated the antishort to 5 minutes no excursions! any thoughts on why this works beyond whats in the manual?

    Name:  antishort update april 7th.jpg
Views: 91
Size:  39.6 KB

  10. #29
    Join Date
    Jun 2002
    Location
    Ft. Leonard Wood/Waynesville Missouri
    Posts
    2,562
    Post Likes
    Short cycling keeping the compressor on I would think. PC you are the hero bro.

  11. #30
    Join Date
    Jun 2002
    Location
    Ft. Leonard Wood/Waynesville Missouri
    Posts
    2,562
    Post Likes
    The default is 5 too start.

  12. #31
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Where exactly do the sensors "hang from" the evaporators?

    Are the sensor probes always directly in the inlet air stream to the evaporators?

    PHM
    ------


    Quote Originally Posted by PharmaPhridge View Post
    . . . the units are . . . each controlled by their own Emerson controller 16e09101. The sensor probes hang from the evaps.

    Periodically, we are observing overcooling from a setpoint of 5C +/- 1C to about -6C. . . .
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  13. #32
    Join Date
    Mar 2022
    Posts
    11
    Post Likes
    Thread Starter
    They hang from the sides...Name:  temp probe 1.jpg
Views: 79
Size:  58.8 KBName:  temp probe 2.jpg
Views: 63
Size:  51.4 KB

  14. #33
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Problem: System operates below setpoint at times.

    Possibilities: Either the compressor refrigeration does not respond to the temperature controller contacts opening - or the temperature controller contacts do not open at the lower set point.

    A way to determine which would be an independently powered latch-out-relay circuit across the temperature controller contacts with the NC relay contacts powering a light. If you see a too-cold spike in the temperature monitoring graph and the light is out - the contacts opened and the problem keeping the compressor operating to cool below set point is elsewhere.

    Is this WIC inside a building or is it an exterior unit?

    Can you correlate the too-cold-spike issue with the ambient and/or weather conditions in any pattern-establishing way?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  15. #34
    Join Date
    Jun 2002
    Location
    Ft. Leonard Wood/Waynesville Missouri
    Posts
    2,562
    Post Likes
    Close enough to return. But I would have put a union in that drain for cleaning.

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •