    Downsizing a Freezer

    So this customer has a 18x6 Freezer , and a 9x6 Cooler

    He wants me to move the Freezer Fan Coil over to the Cooler ... so the 9x6 will suddenly become the Freezer

    Then buy a whole new system for the 18x6 which will now be a Cooler

    Will the Oversized Freezer set-up have any ill effects ? ?
    If you never encounter anything in your community that offends you , then you aren't living in a Free Society

  2. #2
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,729
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    So this customer has a 18x6 Freezer , and a 9x6 Cooler

    He wants me to move the Freezer Fan Coil over to the Cooler ... so the 9x6 will suddenly become the Freezer

    Then buy a whole new system for the 18x6 which will now be a Cooler

    Will the Oversized Freezer set-up have any ill effects ? ?
    Only thing I can think of is short run times.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  3. #3
    Join Date
    Dec 2007
    Location
    East Coast
    Posts
    29
    Post Likes
    You'll have shorter run times like WT70 said. You also need to make sure the existing cooler has an insulated floor, should have at least 4" walls (preferably 5), heated vent, door and frame.

  4. #4
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    10,463
    Post Likes
    Thread Starter
    Yeah I have to move the door and wiring and stuff ... its gonna suck
    If you never encounter anything in your community that offends you , then you aren't living in a Free Society

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    36,296
    Post Likes
    Can it be done YES. Keep a wide differential on the t-stat to prevent short cycling.

    Should it be done, NO.

    Change the gas from R-404A to R-134A and get new equipment for the 9 X 6 freezer.

  6. #6
    Join Date
    Jan 2010
    Posts
    28,024
    Post Likes
    Wait !
    Is this that freezer/cooler combo ?

  7. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    36,296
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Wait !
    Is this that freezer/cooler combo ?
    I hope 2 separate boxes.

    Someone's going to be surprised trying to release those cam locks.

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    10,463
    Post Likes
    Thread Starter
    yeah you walk through the 9x6 cooler to access the freezer door

    He also wants the door moved to the Side .... so he wont have to walk through cooler ... so each will be accessible on their own

    Its gonna suck big balls
    If you never encounter anything in your community that offends you , then you aren't living in a Free Society

  9. #9
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    10,463
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post

    Change the gas from R-404A to R-134A and get new equipment for the 9 X 6 freezer.
    hmm ....
    If you never encounter anything in your community that offends you , then you aren't living in a Free Society

  10. #10
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    10,463
    Post Likes
    Thread Starter
    I didnt take pics of box

    It has those stupid quick connects ...awesome
    Attached Images Attached Images  
    If you never encounter anything in your community that offends you , then you aren't living in a Free Society

  11. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    36,296
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    yeah you walk through the 9x6 cooler to access the freezer door

    He also wants the door moved to the Side .... so he wont have to walk through cooler ... so each will be accessible on their own

    Its gonna suck big balls
    I don't see that being possible. The frames, floor and ceiling panels are designed for specific locations so the cam locks line up.

    Never had luck releasing those locks after a few years. Condensation rusts them in place.

  12. #12
    Join Date
    Jan 2010
    Posts
    28,024
    Post Likes
    Yeah you might want to check a few cam locks before quoting the job.
    Those condensing units look newer.
    Can I have the one he's getting rid of ?

  13. Likes Snapperhead, mofotech liked this post.
  14. #13
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    17,100
    Post Likes
    What you need to be concerned with is the cooler box becoming low temp. Does it have an insulated floor? Is the door heated?

    If no to either, you're asking for trouble.

  15. Likes mofotech liked this post.
  16. #14
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    17,100
    Post Likes
    Quote Originally Posted by lovetowork View Post
    You'll have shorter run times like WT70 said. You also need to make sure the existing cooler has an insulated floor, should have at least 4" walls (preferably 5), heated vent, door and frame.
    Please update your email address in your profile. I had to remove the old one because it was bouncing.

    Thanks

  17. #15
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    2,859
    Post Likes
    A new box might be cheaper and quicker in the long run. Too many things going on that could go really bad.
    “A dying culture invariably exhibits personal rudeness. Bad manners. Lack of consideration for others in minor matters. A loss of politeness, of gentle manners, is more significant than is a riot.”
    ― Robert A. Heinlein

  18. #16
    Join Date
    Jan 2010
    Posts
    28,024
    Post Likes
    Quote Originally Posted by pecmsg View Post
    I don't see that being possible. The frames, floor and ceiling panels are designed for specific locations so the cam locks line up.
    and then there's this ☝🏻

  19. #17
    Join Date
    Aug 2019
    Posts
    44
    Post Likes
    I would not do it....for many reasons..One would be a non insulated floor and a door heater.... what he customer is asking you to do....will not work in my opinion

  20. #18
    Join Date
    Jan 2010
    Posts
    28,024
    Post Likes
    Wait !
    Did he say it didn't have a floor ?

  21. #19
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    10,463
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post

    Never had luck releasing those locks after a few years. Condensation rusts them in place.
    Has anyone figured how to get them apart ?
    If you never encounter anything in your community that offends you , then you aren't living in a Free Society

  22. #20
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    10,463
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    Wait !
    Did he say it didn't have a floor ?
    I didnt pay attention ... but I wanna say those walk through boxes usually do have floors in Both
    If you never encounter anything in your community that offends you , then you aren't living in a Free Society