Thread: Walk in cooler low head and suction

  1. #1
    Join Date
    Dec 2021
    Location
    Eastern Shore of Virginia
    Posts
    11
    Post Likes

    Walk in cooler low head and suction

    Hello. I am an HVAC contractor. I haven't done much refer work, however I recently installed a walk in cooler system. My issue has become a low head and suction pressure. (140/15). The system is a 404A unit. I installed a 3/8" liquid line and a 5/8" suction line. I have a solid ice cube at my txv, and cannot get either pressure to rise. Sight glass is clear, and walk in cooler drops to 39 degrees with no problem. I did adjust the pressure switch just to keep it going because if it satisfies the t stat, it begins to cycle of and on at next start up. It then just short cycles continuously on the LPS. Any advice would be helpful. Thanks!

  2. #2
    Join Date
    Sep 2016
    Location
    PL In New York
    Posts
    953
    Post Likes
    Quote Originally Posted by Dewey HVAC View Post
    Hello. I am an HVAC contractor. I haven't done much refer work, however I recently installed a walk in cooler system. My issue has become a low head and suction pressure. (140/15). The system is a 404A unit. I installed a 3/8" liquid line and a 5/8" suction line. I have a solid ice cube at my txv, and cannot get either pressure to rise. Sight glass is clear, and walk in cooler drops to 39 degrees with no problem. I did adjust the pressure switch just to keep it going because if it satisfies the t stat, it begins to cycle of and on at next start up. It then just short cycles continuously on the LPS. Any advice would be helpful. Thanks!
    What is the model and serial number of the condensing unit/ evap coil?
    What is the superheat value at the compressor?

  3. #3
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Is the condenser indoors or outdoors and what is the ambient temp?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Superheat and Sub Cooling #'s.

  5. #5
    Join Date
    Sep 2016
    Location
    PL In New York
    Posts
    953
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Superheat and Sub Cooling #'s.
    Restriction before/at the metering device? That's my guess. What's he mean when he says "i adjusted the lps to keep it going">? Is it running continuous now? I confused

  6. #6
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    At 15#'s suction I could see it cycling on low pressure however if this is a pump down system I would probably set in closer to 5 psig.
    How many pounds of refrigerant did you put in and what HP is the compressor ?
    Of course knowing the answers to the other questions presented here sure would help eliminate some guesswork 😉

  7. #7
    Join Date
    Dec 2021
    Location
    Eastern Shore of Virginia
    Posts
    11
    Post Likes
    Thread Starter
    Condensing unit MOD# CCH0010MCACZ SER#T21M21245
    Evaporator MOD# BEL0115AS6AMAD SER# T21K23890
    Not sure about super heat at this moment.

  8. #8
    Join Date
    Dec 2021
    Location
    Eastern Shore of Virginia
    Posts
    11
    Post Likes
    Thread Starter

    Thanks for your time and continued advice

    Condensing unit MOD# CCH0010MCACZ SER#T21M21245
    Evaporator MOD# BEL0115AS6AMAD SER# T21K23890
    Not sure about super heat at this moment.
    Condensing unit is outdoors... roof top
    Used an initial charge of 9 lbs, however, I will say I have added quit a bit more trying to bring the pressures up.
    On initial start up, I was not having this issue, pressures seemed a bit low, then suddenly this happened.
    I adjusted the LPS because when the unit starts, it will cycle off and on rapidly because the suction pressure will not rise. so, I adjusted the differential so it will run.
    It is a pump down system, and it is cycling on the t stat as we speak. in other words, it is operating, but not properly.
    ALSO, I know, I know from all of you... I have made several mistakes, but I want to hear about them as I love learning.

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Quote Originally Posted by Dewey HVAC View Post
    Condensing unit MOD# CCH0010MCACZ SER#T21M21245
    Evaporator MOD# BEL0115AS6AMAD SER# T21K23890
    Not sure about super heat at this moment.
    Condensing unit is outdoors... roof top
    Used an initial charge of 9 lbs, however, I will say I have added quit a bit more trying to bring the pressures up.
    On initial start up, I was not having this issue, pressures seemed a bit low, then suddenly this happened.
    I adjusted the LPS because when the unit starts, it will cycle off and on rapidly because the suction pressure will not rise. so, I adjusted the differential so it will run.
    It is a pump down system, and it is cycling on the t stat as we speak. in other words, it is operating, but not properly.
    ALSO, I know, I know from all of you... I have made several mistakes, but I want to hear about them as I love learning.
    Thats not how you do it!!!Once the SG is clear Thats IT.

    We need the SH readings at the outlet of the evaporator and about 6" before the compressor.
    Take temperature readings across the drier. Should be less then 1°F.
    Is this a Pump Down System? I hope so.

    The LP control was doing its job.

  10. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes

  11. #11
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Standard unit is micro channel with a 140 headmaster. At this point it sounds like evap is starving.
    https://products.heatcraftrpd.com/dA...f/CC-PC-PL.pdf
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  12. #12
    Join Date
    Dec 2021
    Location
    Eastern Shore of Virginia
    Posts
    11
    Post Likes
    Thread Starter
    Ordered the book. Thanks!!!

  13. #13
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    What's that evaporator branded ?

  14. #14
    Join Date
    Dec 2021
    Location
    Eastern Shore of Virginia
    Posts
    11
    Post Likes
    Thread Starter
    heatcraft

  15. #15
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    There is probly a screen at the TXV .... and it might be dirty

    But are you sure the sight glass is full .... not completely empty ? Sometimes they will trick you

    Whats the outdoor temp ?
    Tell your Cat I said "Psst Psst Psst"

    It seems like everywhere I go the AC is broken

  16. #16
    Join Date
    Sep 2016
    Location
    PL In New York
    Posts
    953
    Post Likes
    Quote Originally Posted by Dewey HVAC View Post
    heatcraft
    Txv probably is flare. Pump the system down and remove the liquid line connection from the valve. It might have a strainer/screen on the 3/8 inlet that is plugged up. If the system is running a high suction superheat, there is not an adequate amount liquid being distributed to the coil, which would account for your low suction pressure, low coil temp and high suction superheat if present.

  17. #17
    Join Date
    Sep 2016
    Location
    PL In New York
    Posts
    953
    Post Likes
    During the initial setup,

    Did you use a dry nitrogen purge while making connections?

    Did you perform a triple evacuation and use dry nitrogen to break each vacuum?

    Moisture in the system may cause some headaches.

  18. #18
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    What TXV is in the evap?

  19. #19
    Join Date
    Dec 2021
    Location
    Eastern Shore of Virginia
    Posts
    11
    Post Likes
    Thread Starter
    Yes, I purged, pressure tested. And triple evacuated with nitrogen. I am very particular about the installation of equipment. Not that it makes me special, but just to explain how particular I am, I average an install of air conditioning equipment per day. Whether it be a heat pump, A/C, furnace, etc. I have not had a call back in over 5 years. My point... I applied all the specific install techniques to this install as I do to all others. I have only installed one other refer unit before though, and it was much more clear cut than this. It was pretty much a hook up and go. I also feel there is a restriction at the TXV. It is sweat on, and not sure what to do other than maybe cut the line and try to blow nitrogen back through it. ??

  20. #20
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    If this is a regular (non EEV) TXV then the TXV needs a higher minimum hiside pressure.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •