Hvac mode commanded to fanOnly?
Sent from my Pixel 4a using Tapatalk
Anyone ever see these things go sideways and come up with an active setpoint (TempControlPt) of 256F?
Had a building recently that I suspect took a power glitch or something along those lines that really caused some problems. Its 3x Excel 10s, all but one had a 256F active setpoint even though occ setpoints where all normal. Also 5x Trane Intellipak units with LCI cards that went into emergency stop - comms failure. That's all that's on this lon trunk and all but one unit went bonkers. System has been running fine for a few years now, so outside of lighting, power issue not sure what to make of it.
Dug around in the intellipak manuals and I don't even see the fault they told me listed. Most of their com faults in the books name the specific module and are all auto reset.
Propagating the formula. http://www.noagendashow.com/
Hvac mode commanded to fanOnly?
Sent from my Pixel 4a using Tapatalk
They all look to be set for hvacAuto. That point wasn't even pulled into the Niagara database till I just did to check it.
Looking at the logs, they didn't actually start heating but they did stop cooling which caused the ruckus.