Results 1 to 16 of 16

Thread: Small HVAC Should Have A Non-Plenum Returns only?

  1. #1
    Join Date
    Nov 2020
    Posts
    8
    Post Likes

    Small HVAC Should Have A Non-Plenum Returns only?

    Hi,

    I have a question. I recently had an hvac tech tell me that small HVACs should have non-plenum return(s) because plenum returns on small roof top units (example 6-tons) are virtually ineffective. Is this true?

  2. #2
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,287
    Post Likes
    .
    Have him put that in writing, signed and dated. Then find a new guy.
    ..
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  3. #3
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    9,034
    Post Likes
    It appear he is saying to pull return air into the rooftop unit (package unit) from outside. That’s so wrong!
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/


    Site member map HERE!

  4. #4
    Join Date
    Nov 2020
    Posts
    8
    Post Likes
    Thread Starter
    Hi Kdean1,

    He is saying to pull return air into the rooftop unit from the occupied space.

  5. #5
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    9,034
    Post Likes
    Quote Originally Posted by calettso View Post
    Hi Kdean1,

    He is saying to pull return air into the rooftop unit from the occupied space.
    Then there must be a trunk through the attic, or if commercial, space above the drop ceiling. If it is a drop ceiling used as a return, all wiring in that space must be plenum rated.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/


    Site member map HERE!

  6. #6
    Join Date
    Nov 2020
    Posts
    8
    Post Likes
    Thread Starter
    I was thinking it was a rather interesting response. I then started thinking he meant, given the facility we were discussing, it was virtually useless. So here is some background information:

    - This relatively new (less than 1 year) commercial facility has a humidity problem that is obvious during the warmest most humid days of the summer.
    - From floor to drop ceiling 10'.
    - From floor to roof 20'.

    I am not sure if he is saying given the vast amount of space above, it is virtually useless.

    I believe the humidity problem is because the facility is not properly sealed to prevent external air from being sucked in from outside (cracks and small spaces in the walls and roof). I say that because the relative humidity in the facility on the day I was there was 66%.

  7. #7
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,287
    Post Likes
    .
    What region of the www is this building located?
    Was it a quick build, was the concrete green when built?
    ..
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  8. #8
    Join Date
    Nov 2020
    Posts
    8
    Post Likes
    Thread Starter
    Hi Sleuth,

    - The facility is located in metro Atlanta.
    - Not aware of it being a quick build and concrete green when built. If I had to guess I would say no to both.

  9. #9
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,287
    Post Likes
    .
    This building has been occupied for one year? And has a suspended ceiling? And is in Hot Lanta.
    ..
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  10. #10
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    15,406
    Post Likes
    Is this unit sucking air free from between roof and ceiling? If so he is probably saying that putting a ducted return to below the ceiling would make no difference which would be wrong.

  11. Likes kdean1 liked this post.
  12. #11
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,287
    Post Likes
    .
    You can ask for the manufacturer's install book or even look it up yourself. Just need model # and time to digest it.

    We experimented with whole "house" plenums" in the 70s and that didn't go well....
    ..
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  13. Likes kdean1 liked this post.
  14. #12
    Join Date
    Nov 2020
    Posts
    8
    Post Likes
    Thread Starter
    Hi BNME8EZ,

    Thanks for responding. No he is saying the ducted return to the below ceiling would be better because the non-ducted (plenum) is useless.

  15. #13
    Join Date
    Nov 2020
    Posts
    8
    Post Likes
    Thread Starter
    Hi Sleuth,

    Perhaps this is what the tech is saying. The whole "house" plenums in a hot environment, especially with the vast amount of space above the drop ceiling, is useless. If this is what he is saying, I can better understand his statement.

  16. #14
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,287
    Post Likes
    .
    In the 70s it was supply side...unfathomable on return side.
    ..
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  17. #15
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    15,406
    Post Likes
    Quote Originally Posted by Sleuth View Post
    .
    In the 70s it was supply side...unfathomable on return side.
    ..
    We did a couple houses in the late 70's early 80's when I was just starting in the trade that had web truss joists. They sheetrock finished all the ceiling in the basement and the space in the web truss was used as return. It seemed to have worked well until someone took some ceiling down and didn't put it back.

  18. #16
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,219
    Post Likes
    Quote Originally Posted by calettso View Post
    Hi BNME8EZ,

    Thanks for responding. No he is saying the ducted return to the below ceiling would be better because the non-ducted (plenum) is useless.
    That makes sense. With no direct connection to the conditioned space the rooftop unit would be pulling the hottest air from right under the roof deck 10' above the suspended ceiling.

    As for a humidity problem a 6 ton unit should have an economizer on it and might be pulling in too much outside air when the humidity is high outside, then you add to that the return is pulling from above the ceiling and the AC might not be running enough to dehumidify the extra humidity from outside due to the economizer not being adjusted correctly OR someone didn't design/spec the job correctly.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.