We just had a Mitsubishi Hyper-Heat mini split system installed, with 5 head units. We are noticing some behavior, that doesn't seem logical. Here is a quick summary of our system:
Outdoor unit: MXZ-5C42NAHZ2 (42,000 btu)
Branch box 1 - two head units:
Bedroom A - MSZ-GL06NA (6,000 btu)
Bedroom B - MSZ-GL06NA (6,000 btu)
Branch box 2 - three head units:
Living room - MSZ-GL18NA (18,000 btu)
Basement - MSZ-GL06NA (6,000 btu)
Bedroom C - MSZ-GL06NA (6,000 btu)
What seems to happen, is that if one head unit is calling for heat, all 5 heads appear to have hot refrigerant circulating through them, even if they are powered off, or set at a temperature lower than the room temperature. Should this be the case, or are the branch boxes supposed to direct the refrigerant only to the head unit(s) that are on and heating?
The effect that I am wondering about is this: Let's say one unit, the living room, for example, is set to 70, and the room temperature is 66, it will be heating (with both indicator lights lit). If the unit in bedroom A, which is on the other branch box, is set to 65, while the room is already 70+ (because it is upstairs and heat rises), it will have the fan running at low speed, because it is idle, but the air coming out of it is quite hot, continuing to increase the room temperature when it shouldn't. At the same time, the unit in the basement is powered off, but if you put your hand on top, it is noticeably warm, as well.
Why would all 5 units have the hot refrigerant circulating through them, when only one unit should be putting out heat? It doesn't seem very efficient, and it doesn't allow for accurate control of the temperature in the separate rooms/zones. What is the point of the branch boxes? Don't they have valves/solenoids to direct the refrigerant to the heads that are running?
Thanks for any input or explanation you can provide.
Outdoor unit: MXZ-5C42NAHZ2 (42,000 btu)
Branch box 1 - two head units:
Bedroom A - MSZ-GL06NA (6,000 btu)
Bedroom B - MSZ-GL06NA (6,000 btu)
Branch box 2 - three head units:
Living room - MSZ-GL18NA (18,000 btu)
Basement - MSZ-GL06NA (6,000 btu)
Bedroom C - MSZ-GL06NA (6,000 btu)
What seems to happen, is that if one head unit is calling for heat, all 5 heads appear to have hot refrigerant circulating through them, even if they are powered off, or set at a temperature lower than the room temperature. Should this be the case, or are the branch boxes supposed to direct the refrigerant only to the head unit(s) that are on and heating?
The effect that I am wondering about is this: Let's say one unit, the living room, for example, is set to 70, and the room temperature is 66, it will be heating (with both indicator lights lit). If the unit in bedroom A, which is on the other branch box, is set to 65, while the room is already 70+ (because it is upstairs and heat rises), it will have the fan running at low speed, because it is idle, but the air coming out of it is quite hot, continuing to increase the room temperature when it shouldn't. At the same time, the unit in the basement is powered off, but if you put your hand on top, it is noticeably warm, as well.
Why would all 5 units have the hot refrigerant circulating through them, when only one unit should be putting out heat? It doesn't seem very efficient, and it doesn't allow for accurate control of the temperature in the separate rooms/zones. What is the point of the branch boxes? Don't they have valves/solenoids to direct the refrigerant to the heads that are running?
Thanks for any input or explanation you can provide.