    Isolation transformer and GFCI

    I have an application where I need a non-GFCI 115V outlet for testing purposes in an environment where I only have GFCIs. If I had a 1:1 isolation transformer with the primary plugged into a GFCI and the secondary side plugged into my non-GFCI application, would the GFCI on the primary side trip?

    This is the transformer I was planning on using:
    https://www.hammfg.com/part/171G?referer=1015
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

  2. #2
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    10,112
    Post Likes
    I've thrown several GFCI's into the trash and put a regular receptacle back - for instance - when they turn off a cooler for no reason , and all of the food has to be thrown out

    I don't write much on the invoice tho ….instead ... I write it up as "performed maintenance" on a cooler

  3. #3
    Join Date
    Sep 2012
    Location
    Perris, CA
    Posts
    53
    Post Likes
    You can wire a secondary outlet and no have it GFCI protected. GFCI are good to have, but can be a pain in the rear end when they fail time and time again.

  4. #4
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    7,421
    Post Likes
    Thread Starter
    I appreciate the replies. Unfortunately, I will not be allowed the option of replacing the outlets. Trying to find a work around for temporary use in many sites.

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    10,112
    Post Likes
    Go to the Main Panel and use your jumpers

  6. #6
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    7,421
    Post Likes
    Thread Starter
    I would use that option but the whole point of the transformer is because the main power is disconnected. The York chillers I am working on need to be powered down at the MCC bucket and then I can power it up with 115V to troubleshoot and test by keeping the controls alive without the 460V safety issue. Unfortunately, the factory hasn’t been of any help on this yet.

  7. #7
    Join Date
    Sep 2012
    Location
    Perris, CA
    Posts
    53
    Post Likes
    Can you use your jumpers by pulling out the outlet? Temporaryly install a regular outlet.

  8. #8
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    7,421
    Post Likes
    Thread Starter
    Quote Originally Posted by emelio67 View Post
    Can you use your jumpers by pulling out the outlet? Temporaryly install a regular outlet.
    Maybe. I think the GCFI would still trip. I was just looking for something quick and simple like the isolation transformer. It already has the plug-ins on it. Of course, only if it would work.

  9. #9
    Join Date
    Sep 2012
    Location
    Perris, CA
    Posts
    53
    Post Likes
    Are we talking about a GFCI breaker or outlet? My mistake I assumed we were talking about a outlet.

  10. #10
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    7,421
    Post Likes
    Thread Starter
    GFCI outlet to transformer to standard outlet

  11. #11
    Join Date
    Jan 2001
    Posts
    28,534
    Post Likes
    Cant you run an extension cord from a non gfci outlet somewhere.
    The bible is my constitution and the constitution is my bible.

    WE THE PEOPLE refers to THEM and not YOU.

    B I N G O…. bingooooo

  12. #12
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name.
    Posts
    13,437
    Post Likes
    Quote Originally Posted by corny View Post
    Cant you run an extension cord from a non gfci outlet somewhere.
    Not if there cannot be a non GFCI outlet by code. Thankfully my state is probably at least 10 years out on adopting that code.
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.