    Mini Splits and required voltage

    I have an apartment complex that runs an ageing Geothermal heating and cooling system, I want to shut this system down and install mini split units in each apartment. The current systems heat pumps all run on 277 volts, there is 480 volts at the panel. The current transformer I have is at capacity and I can't install mini splits that run on 240. (duh) Is there a mini split unit I can get here in the states that runs on 480 volts?

  2. #2
    Join Date
    Feb 2018
    Location
    Bay Area, Ca
    Posts
    1,917
    Post Likes
    Not that I'm aware of. You can do a complex system that could work(big $$$$$$) but the FCU's still run on 240V.

    Sent from my SM-N960U using Tapatalk

  3. #3
    Join Date
    Jan 2010
    Posts
    25,068
    Post Likes
    How many amps is your 480 volts ?

  4. #4
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    4,535
    Post Likes
    Just split one leg into 2 legs and wire nut off the other...duh!!!!
    "Life, Liberty, and Levin!"

  5. #5
    Join Date
    Feb 2018
    Location
    Bay Area, Ca
    Posts
    1,917
    Post Likes
    Yeah. And the merry little leprechaun will come and install it for you.

    Sent from my SM-N960U using Tapatalk

  6. #6
    Join Date
    Jan 2010
    Posts
    25,068
    Post Likes
    .
    Attached Images Attached Images  

  7. #7
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    8,539
    Post Likes
    Your cheapest option is probably going to be replace the geo.

    Otherwise your looking at a VRF system.

  8. #8
    Join Date
    Jun 2019
    Posts
    1,275
    Post Likes
    you need a transformer. Maybe some units have a separate power supply inside not tied to the motherboard but I would not bet on it. Will cost you more and you have no warranty.

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    34,783
    Post Likes
    Quote Originally Posted by gustavhorna View Post
    you need a transformer. Maybe some units have a separate power supply inside not tied to the motherboard but I would not bet on it. Will cost you more and you have no warranty.
    Why No Warranty?

  10. #10
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    4,049
    Post Likes
    Quote Originally Posted by ElderSkippy View Post
    I have an apartment complex that runs an ageing Geothermal heating and cooling system, I want to shut this system down and install mini split units in each apartment. The current systems heat pumps all run on 277 volts, there is 480 volts at the panel. The current transformer I have is at capacity and I can't install mini splits that run on 240. (duh) Is there a mini split unit I can get here in the states that runs on 480 volts?
    I don't have anything to add, but are you saying each apartment has a 480V breaker box in their apartment? If so, does each apartment also have a transformer feeding 230/120V to another breaker panel? I don't work in many apartments, but this seems a little unusual to me. Please clarify, just for my own curiosity. Thanks.
    If at First You Don't Succeed, Skydiving Is Not for You.

  11. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    34,783
    Post Likes
    Seeing how Heat is required Im ASSUMING separate supplies for the HVAC then dropped down to lighting and others.
    Now it could be metered with the A/C or just the lower voltage if metered at all?

  12. #12
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    10,877
    Post Likes
    Unless it's bad broke it's almost always cheaper to fix than replace.
    An apartment would probably require 2 or maybe 3 air sections depending on layout, wall mount or cassettes. Can't talk $$ here. Then there's the electric service, piping add up.
    In it's day did the geothermal perform OK? How broke is it?
    Give me a relay with big enough contacts, and I'll run the world!

    You can be anything you want......As long as you don't suck at it.