    Hello, I have an ERV the user manual states to balance fresh air at 50 CFM needs to be at 35 Pa. The manometers I see say kPa? It's a Panasonic Intellibalance 100 ERV page 14 of their manual has a balancing chart but it says measure across ports with a manometer top of the list says (Pa) and numbers say 50 CFM fresh air should read 35. So its confusing since almost all the Manometers I see say kPa... not Pa... so how do I measure and which manometer do I buy? Do I just need one that measure kPa but it has to have x.xxx ( 3 levels of measurement and it should read x.035 ?
    Thanks,
    Jan 2015
    San Diego, CA
    Quote Originally Posted by cbednarczyk View Post
    Thanks,
    Yes one way would be to get a manometer that displays Pa in a suitable manner. 35 Pa is about 0.14" WC so you can either measure in Pa or if it is preferable measure in " WC. Since manometers measure pressure typically in this sort of range even though it says kPa it should be capable of displaying 35 Pa accurately.
    I would check the manometer specs on the units and display ranges before buying to make sure it can do what you want.
    Sep 2021
    So you would need a manometer that would display kPA down to .035 Kpa to get 35 Pa? Is that correct?
    Jan 2015
    San Diego, CA
    The actual unit of measurement is Pa - the "k" is just a 1000 multiplier. Manometers are designed to measure down to very low pressures - for example the micro manometer on my flowhood can measure in kPa as well as Pa.
    Whatever manometer you plan to buy make sure it can either measure in Pa or has at least 3 digits after the decimal point on the kPa scale. As I said another option is to get a manometer that can measure " WC and convert from Pa to " WC.
    VA
    I believe you’re looking for a micro-manometer $$$
    "The only true wisdom is in knowing you know nothing" Socrates
    Jun 2021
    Thanks,
    I think that you need a Magnehelic, I have attached examples found on google.
    Mechanical:
    https://www.dwyer-inst.com/Product/P...ges/Series2000
    Digital:
    https://www.dwyer-inst.com/Product/P.../SeriesDM-1000