Thread: Potential Root Causes? Holds pressure but doesn't hold vacuum

  1. #1
    Join Date
    Sep 2021
    Posts
    5
    Post Likes

    Potential Root Causes? Holds pressure but doesn't hold vacuum

    Hi,

    New forum member so please be gentle with me....

    I'm looking for theories from those more experienced than myself as to what might be causing an odd behavior in a refrigeration system that my team is working on. We've conducted pressure hold tests using nitrogen gas for 24hrs within our system at ~100 psi and have observed no discernable leak from the system. This system has electronic pressure sensors throughout so we've been able to log pressure data overnight at a frequency of every 30 seconds and are not seeing any signs of a pressure drop. Secondly we've been applying leak detector to a known problem area and this is also exhibiting no signs of a leak under positive pressure.

    However, when preparing to fill the system and pulling vacuum, we are not seeing the micron level stabilize when capping the system. The unit was capped over the weekend, and the micron gauge has risen to >60000 microns. Considering that the maximum pressure differential created under vacuum is ~14.7psi, I'm at a loss as to how we can observe a >1 psi pressure shift under vacuum, but when under far greater pos. pressure differential we are not observing any shift.

    Some additional color
    - This system was left open in an office environment for a few months. Has anyone seen issues similar to this as a result of a filter dryer being spent?

    Anyway, I'm not an HVAC expert and I'm just trying to get a sense for those that are, if you've observed similarly confusing situations before and if so, what the problem was to aid myself and team in trying to hunt down our issue.

    Thanks!

  2. #2
    Hurst11 is offline Professional Member/Membership Committee
    Join Date
    May 2020
    Location
    Haskell Oklahoma
    Posts
    1,529
    Post Likes
    What kinda system are you working on and what is your evacuation setup? Are you pulling through a manifold or do you have an actual vacuum set up.

  3. #3
    Join Date
    Apr 2015
    Location
    Kent, OH
    Posts
    25
    Post Likes
    I've had issues with filter driers holding on to moisture or refrigerant and causing evacuations to take a lot longer. It could be slowly off gassing and raising your pressure while it's in a vacuum but you wouldn't see anything while it's pressurized. I would definitely change the driers and probably the oil too if the system had been open a while, especially if it's POE or another synthetic.

  4. Likes heatingman, Patech liked this post.
  5. #4
    Join Date
    Sep 2021
    Posts
    5
    Post Likes
    Thread Starter
    So unfortunately I can't divulge much about the system due the nature of what it is. What I can share is that no manifold is being used and vacuum and filling is being accessed via a core removal tool. This system does not include any oil since the refrigerant circulation method is 'non-traditional' and does not use a compressor.

    We've been pulling vacuum down to the ~60 micron level for probably 24+ combined hours now, spread over a ~6 day period and we're still seeing the same issue. Honestly, due to the intended use and expected life of the system, I'm pretty close to just filling the darn thing with refrigerant. Not being an expert in the space, my limited understanding is that there can be a number of factors that can contribute to a rising vacuum pressure. I believe we've ruled out the presence of a leak due to the positive pressure testing, so I'm curious if anyone has experienced any 'gotcha' situations where a positive pressure test over a time scale of significance, yielded a false positive leak pass/fail result that a vacuum test was able to catch.

  6. #5
    Join Date
    Sep 2012
    Location
    USA
    Posts
    7,706
    Post Likes
    Quote Originally Posted by Inclag View Post
    So unfortunately I can't divulge much about the system due the nature of what it is. What I can share is that no manifold is being used and vacuum and filling is being accessed via a core removal tool. This system does not include any oil since the refrigerant circulation method is 'non-traditional' and does not use a compressor.

    We've been pulling vacuum down to the ~60 micron level for probably 24+ combined hours now, spread over a ~6 day period and we're still seeing the same issue. Honestly, due to the intended use and expected life of the system, I'm pretty close to just filling the darn thing with refrigerant. Not being an expert in the space, my limited understanding is that there can be a number of factors that can contribute to a rising vacuum pressure. I believe we've ruled out the presence of a leak due to the positive pressure testing, so I'm curious if anyone has experienced any 'gotcha' situations where a positive pressure test over a time scale of significance, yielded a false positive leak pass/fail result that a vacuum test was able to catch.
    So..... you can actually pull a vacuum to fast....

    It's rare but if you pull a vacuum to fast you can cause ice to form.

    Your microns will rise as the ice melts.

    Who’s to blame?... if you’re looking for the guilty, you need only look into a mirror. I know why you did it. I know you were afraid. Who wouldn’t be? War, terror, disease. There were a myriad of problems which conspired to corrupt your reason and rob you of your common sense. Fear got the best of you, and in your panic you turned to the now high chancellor, Adam Sutler. He promised you order, he promised you peace, and all he demanded in return was your silent, obedient consent. V for Vendetta

  7. #6
    Join Date
    Sep 2012
    Location
    USA
    Posts
    7,706
    Post Likes
    Quote Originally Posted by Inclag View Post
    So unfortunately I can't divulge much about the system due the nature of what it is. What I can share is that no manifold is being used and vacuum and filling is being accessed via a core removal tool. This system does not include any oil since the refrigerant circulation method is 'non-traditional' and does not use a compressor.

    We've been pulling vacuum down to the ~60 micron level for probably 24+ combined hours now, spread over a ~6 day period and we're still seeing the same issue. Honestly, due to the intended use and expected life of the system, I'm pretty close to just filling the darn thing with refrigerant. Not being an expert in the space, my limited understanding is that there can be a number of factors that can contribute to a rising vacuum pressure. I believe we've ruled out the presence of a leak due to the positive pressure testing, so I'm curious if anyone has experienced any 'gotcha' situations where a positive pressure test over a time scale of significance, yielded a false positive leak pass/fail result that a vacuum test was able to catch.
    sounds like your working on a heat pipe style system.
    Who’s to blame?... if you’re looking for the guilty, you need only look into a mirror. I know why you did it. I know you were afraid. Who wouldn’t be? War, terror, disease. There were a myriad of problems which conspired to corrupt your reason and rob you of your common sense. Fear got the best of you, and in your panic you turned to the now high chancellor, Adam Sutler. He promised you order, he promised you peace, and all he demanded in return was your silent, obedient consent. V for Vendetta

  8. #7
    Join Date
    Sep 2021
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by Elfshadow View Post
    So..... you can actually pull a vacuum to fast....

    It's rare but if you pull a vacuum to fast you can cause ice to form.

    Your microns will rise as the ice melts.
    Thank you. This is beneficial and could be a potential cause. We are generating a sub 500 micron vacuum in extremely short order. Probably easily under 30 seconds.

    Are there methods/modes/tools of regulating the vacuum pull to more like ~15,000 or 12,000 microns? This would presumably boil off any moisture in due time I would imagine. I recognize that purging/replacing the drier is probably the 'correct' solution, but this system that we are working on only has a single access port due to the nature of what it is. If I had my druthers there would be some significant changes in order to increase the workablity of the system, but my team is between a rock and a hard place and a modality of boiling off potential moisture even in light of perhaps the time needed to do this, would be more preferable than pulling things apart. Pulling apart is going to incur risk and human cost/time which isn't something I can tolerate at the moment. A passive mode of connecting a regulated vacuum that incurs sitting and waiting for potential moisture to boil off is far more preferable.

    I'd be willing to give the latter option, if doable, a shot before filling our system.

  9. #8
    Join Date
    Sep 2012
    Location
    USA
    Posts
    7,706
    Post Likes
    Quote Originally Posted by Inclag View Post
    Thank you. This is beneficial and could be a potential cause. We are generating a sub 500 micron vacuum in extremely short order. Probably easily under 30 seconds.

    Are there methods/modes/tools of regulating the vacuum pull to more like ~15,000 or 12,000 microns? This would presumably boil off any moisture in due time I would imagine. I recognize that purging/replacing the drier is probably the 'correct' solution, but this system that we are working on only has a single access port due to the nature of what it is. If I had my druthers there would be some significant changes in order to increase the workablity of the system, but my team is between a rock and a hard place and a modality of boiling off potential moisture even in light of perhaps the time needed to do this, would be more preferable than pulling things apart. Pulling apart is going to incur risk and human cost/time which isn't something I can tolerate at the moment. A passive mode of connecting a regulated vacuum that incurs sitting and waiting for potential moisture to boil off is far more preferable.

    I'd be willing to give the latter option, if doable, a shot before filling our system.
    Triple evacuation and sweep with nitrogen sweeps. If you only have a single port.... you can't really flow nitrogen though. If you have pressure transducers can you pull one out to let you flow nitrogen through.

    Might want to google triple evacuation.

    This a heatpipe or convection system?? Probably won't answer that.

    The triple evacuation is meant to be a means of dehydrating refrigerant tubing in a system that has high water content before refrigerant is introduced. This was and is still used on systems that have the potential for water to freeze while vacuuming.
    Who’s to blame?... if you’re looking for the guilty, you need only look into a mirror. I know why you did it. I know you were afraid. Who wouldn’t be? War, terror, disease. There were a myriad of problems which conspired to corrupt your reason and rob you of your common sense. Fear got the best of you, and in your panic you turned to the now high chancellor, Adam Sutler. He promised you order, he promised you peace, and all he demanded in return was your silent, obedient consent. V for Vendetta

  10. #9
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    “>60000 microns”. ? Not water or moisture at that level.
    If that high, my guess would be a shaft seal or relief valve. System model & type would help……

  11. #10
    Join Date
    Sep 2012
    Location
    USA
    Posts
    7,706
    Post Likes
    Quote Originally Posted by ehsx View Post
    “>60000 microns”. ? Not water or moisture at that level.
    If that high, my guess would be a shaft seal or relief valve. System model & type would help……
    Based on what hes talking this is something at a college or company.

    non-compressor based system that still uses refrigerent.

    Im guessing something using convection. There was a ton of noise around convection based CPU cooling a few years ago.

    Thinking something like this....

    Getting below 500 micro in 60 seconds indicates a very small volume to.

    Last edited by Elfshadow; 09-20-2021 at 06:36 PM.
    Who’s to blame?... if you’re looking for the guilty, you need only look into a mirror. I know why you did it. I know you were afraid. Who wouldn’t be? War, terror, disease. There were a myriad of problems which conspired to corrupt your reason and rob you of your common sense. Fear got the best of you, and in your panic you turned to the now high chancellor, Adam Sutler. He promised you order, he promised you peace, and all he demanded in return was your silent, obedient consent. V for Vendetta

  12. #11
    Join Date
    Oct 2016
    Posts
    3,838
    Post Likes
    I would verify your “set-up” is not leaking.

    Maybe take a pice of 3/4 tubing 10ft long, braze both ends closed, add a service port. Pull that down and make sure it will hold.

    I’ve fought the same battle you are dealing with. Interested to hear if you get it resolved. We replace the little rubber thingys in the hoses as they leak under vacuum but not positive pressure sometimes.

  13. #12
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    For doing a long decay test you need to actually get all of the moisture out of the system.
    It's virtually impossible to just vacuum to 500 microns and blank it off for a day without having an extremely deep vacuum pulled in the first place.
    I have performed long blank off tests. Most of the time in order to legitimately pass the test my pump would need to pull that vacuum for days before blanking off.
    So a legitimate 125 micron reading at blank off time would typically read 350 microns after 72 hours.
    There is no such thing as a quick vacuum for a blank off test longer than 30 minutes

  14. Likes heatingman liked this post.
  15. #13
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    As stated, is this a small volume system?

    If so, that could be the issue in itself.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  16. #14
    Join Date
    Aug 2021
    Location
    Chattahoochee State Mental Hospital
    Posts
    6,390
    Post Likes
    I have seen this problem once. It was a pop off. Would seal under pressure, not so much under vacuum.
    And a poorly brazed connection can seal under pressure, but leak under vacuum.

    Sent from my phone, using that talk thingie.
    .Please consider donating $11 to Tunnels to Towers, a great way to help Veterans, who fought communist ideology all over the world.
    Hail the Republic!

  17. Likes Unlimited1, New Mini-Split liked this post.
  18. #15
    Hurst11 is offline Professional Member/Membership Committee
    Join Date
    May 2020
    Location
    Haskell Oklahoma
    Posts
    1,529
    Post Likes
    Quote Originally Posted by Fla.HP View Post
    I have seen this problem once. It was a pop off. Would seal under pressure, not so much under vacuum.
    And a poorly brazed connection can seal under pressure, but leak under vacuum.

    Sent from my phone, using that talk thingie.
    I’ve never saw that, how does that happen? The braze hold under pressure but leak when not?

  19. Likes R600a liked this post.
  20. #16
    Join Date
    Aug 2021
    Location
    Chattahoochee State Mental Hospital
    Posts
    6,390
    Post Likes
    Just think about what happens to copper joints under stress. From vacuum to full pressure...and the expansion and contractions they go through

    Sent from my phone, using that talk thingie.
    .Please consider donating $11 to Tunnels to Towers, a great way to help Veterans, who fought communist ideology all over the world.
    Hail the Republic!

  21. Likes Unlimited1 liked this post.
  22. #17
    Join Date
    Jun 2019
    Posts
    1,610
    Post Likes
    You are doing something wrong! if you measure pressure this will vary with ambient temperature. You can't have it CONST!
    By the gas equation pV = nRT your pressure will vary over the course of the day, as T does!

    In contrast if you see vacuum decay you HAVE a leak!

  23. #18
    Join Date
    Feb 2014
    Location
    LA LA, CA
    Posts
    272
    Post Likes
    Have you checked your hoses and core tool. Try a little nylog. Most usually my vacuum leaks are at my added connections and not my systems.

    Sent from my Pixel 2 XL using Tapatalk

  24. Likes R600a, New Mini-Split liked this post.
  25. #19
    Join Date
    Jun 2006
    Posts
    1,376
    Post Likes
    Hmm well single access port is going to make it pretty hard to say. I have seen Schrader leak vac that would hold pressure but sounds like you have none.

    Very low volume systems are hard to micron test because the tiny bit of leakage makes a huge impact.

    Core removal tool might be a cause nylon the O rings, the vac gage itself, nylon it's o ring.

    Sorry if it's insulting but if your team is qualified enough to be developing such a system they should be able to handle such a problem with ease.

  26. Likes New Mini-Split liked this post.
  27. #20
    Join Date
    Jun 2006
    Posts
    1,376
    Post Likes
    Nylog not nylon

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •