Thread: Performance issue

  1. #21
    Join Date
    Mar 2015
    Location
    Canada
    Posts
    1,703
    Post Likes
    Quote Originally Posted by ddkk0099 View Post
    No, it is not having
    Then I wouldn't go below 8°f SH. The higher you can keep it, the safer the compressors.

  2. #22
    Join Date
    Mar 2015
    Location
    Canada
    Posts
    1,703
    Post Likes
    BTW, is the software actively calculating the output capacity?

    Have you selected the correct liquid in the software? What liquid are you using? Straight water? Any glycol? Anything else? Are the flow readings also from the software?

    Is this unit actually keeping up and you're just confused about the output capacity difference, or are you needed a bit more capacity?

  3. #23
    Join Date
    Oct 2018
    Posts
    54
    Post Likes
    Thread Starter
    Yes, agree with you.
    Looks to me issue with Evaporator.

  4. #24
    Join Date
    Oct 2018
    Posts
    54
    Post Likes
    Thread Starter
    This is compressor capacity that software is calculating based on operating conditions. Liquid is water.
    I need to have more capacity.

  5. #25
    Join Date
    Jun 2021
    Posts
    18
    Post Likes
    Quote Originally Posted by ddkk0099 View Post
    Hi,

    Currently I am working on 18 TR (63 Kw) chiller system. Operating parameters are as below :

    Suction pressure (Psig) - 100.383
    Discharge pressure (Psig) - 427.092
    Superheat (K)- 8.83
    Subcooling (K)- 10.46
    Flow rate (m3/h) - 8.58
    Water in (Deg C)- 11.8
    Water out (Deg C ) -7.05

    Water capacity that I am geting is 47.63 Kw. When I checked on compressor software, it should deliver around 59 Kw.

    Can anyone help on what can be done to improve capacity of system.
    How do you measure exactly Subcooling?
    Where do you measure liquid pressure and temp?
    What is the nominal flow according to manufacture?

    If you are sure this is the correct data.
    Looks like you Evap approach is a bit high.
    I think you should look inside to make sure evap is clean.
    Check also filter mesh (opening of the filter).

  6. #26
    Join Date
    Jun 2021
    Posts
    18
    Post Likes
    Quote Originally Posted by ishaitz View Post
    How do you measure exactly Subcooling?
    Where do you measure liquid pressure and temp?
    What is the nominal flow according to manufacture?

    If you are sure this is the correct data.
    Looks like you Evap approach is a bit high.
    I think you should look inside to make sure evap is clean.
    Check also filter mesh (opening of the filter).
    Also please share ambient temp and capacity tables of the unit.
    How old is it?

  7. #27
    Join Date
    Oct 2018
    Posts
    54
    Post Likes
    Thread Starter
    Hi, I am having discharge pressure and liquid line temperature. So, I can calculate the subcooling easily. Ambient is 35 deg C and unit is new

  8. #28
    Join Date
    Jun 2021
    Posts
    18
    Post Likes
    Quote Originally Posted by ddkk0099 View Post
    Hi, I am having discharge pressure and liquid line temperature. So, I can calculate the subcooling easily. Ambient is 35 deg C and unit is new
    Please answer fully to all of my questions.
    It is not necessarily accurate due to pressure drop.
    Usually I measure liquid pressure on liquid line it self.

    By the way, any pressure /temp drop on that liquid drier?

  9. #29
    Join Date
    Oct 2018
    Posts
    54
    Post Likes
    Thread Starter
    Subcooling I am measuring by discharge pressure and liquid line temperature jaround 15 cm from condenser outlet.

    I haven't measured air flow rate.

    0.3 K temperature drop across drier which I believe is Ok

  10. #30
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    OK, I have yet to see where the complete model & serial have been divulged; although asked for at least twice. Is the some super "00" spy unit or something?
    Learn to verify what the program is telling you as being true.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  11. Likes supers_5, ishaitz liked this post.
  12. #31
    Join Date
    Mar 2015
    Location
    Canada
    Posts
    1,703
    Post Likes
    Quote Originally Posted by ddkk0099 View Post
    . Liquid is water.
    .
    Open or closed loop? If open, is it a dirty process? Has the water been treated? Filtered?

    I agree that the approach is a tad on the higher side at 13.2°f. Probably could use a cleaning. If there is a water filter, clean /replace it.

    Also SST is a bit low. I wouldn't be surprised if it was shutting off due to freeze protection occasionally.

  13. #32
    Join Date
    Oct 2018
    Posts
    54
    Post Likes
    Thread Starter
    Thanks for your comments. It is in closed loop. So, message coming out is that I need to check on evaporator side.

  14. Likes supers_5 liked this post.
  15. #33
    Join Date
    Mar 2015
    Location
    Canada
    Posts
    1,703
    Post Likes
    Quote Originally Posted by ddkk0099 View Post
    Thanks for your comments. It is in closed loop. So, message coming out is that I need to check on evaporator side.
    Yea.

    Like I said, if there's an inline water filter, change it. If it's a strainer, clean it. What is the rated water flow of the unit?

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •