  1. #21
    Join Date
    Sep 2021
    Posts
    32
    Post Likes
    Thread Starter
    A.C.H. Natural value I don't know, but after they added a few seals to the attic door etc, the hourly value was equivalent to the home square footage, so 1:1, or 4970/4970 heated area.

    Hydro air is a First Co 48MBXR-4HW

    As for your question about introducing air, no idea, I don't think it can. So, I just don't get the infiltration number and how/why it factors into a boiler heated home or doesn't.

    Thanks

  2. #22
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    Quote Originally Posted by NickRizzo View Post

    A.C.H. Natural value I don't know, <--- 0.175
    but after they added a few seals to the attic door etc,
    the hourly value was equivalent to the home square footage, so 1:1,
    or 4970/4970 heated area.
    _____________________ 4,970 cfm50 / 4970 Square Feet Floor Area

    Hydro air is a First Co 48MBXR-4HW

    As for your question about introducing air, no idea, I don't think it can.

    So, I just don't get the infiltration number and how/why it factors into a boiler heated home or doesn't.

    Thanks
    You will have to ask USBoiler for THEIR calculation basis/ methodology.
    ____________ PRESUME BOILER has adequate, separate combustion air.


    Your residence only requires about 80 CFM mechanical ventilation. Ref. ASHRAE 62.2- 2013

    ATTACHMENT
    Attached Images Attached Images  
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  3. #23
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Quote Originally Posted by dan sw fl View Post
    You will have to ask USBoiler for the calculation basis/ methodology.

    Your residence only requires about 80 CFM mechanical ventilation. Ref. ASHRAE 62.2- 2013

    ATTACHMENT
    CFM or CFH

  4. #24
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    Quote Originally Posted by pecmsg View Post
    CFM or CFM
    _ - 2019
    https://ashrae.iwrapper.com/ASHRAE_P.../STD_62.2_2019
    Attached Images Attached Images  
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •