    Inverted traps.

    If your condenser is located below your evaporator is there any point to an inverted P trap at the top of the riser in the suction line? Working on some coolers/freezers and the installation manual calls for suction line traps every 15ft in the riser (which I understand) and an inverted trap at the top of the walk in box and I just didn't quite understand why.

  2. #2
    Join Date
    Mar 2015
    Location
    Canada
    Posts
    1,703
    Post Likes
    Traps are only for rises, not drops. Both inverted and regular.

  3. #3
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    I only use inverted traps if more than one riser to a common header or at condenser gas connection. Insure horizontal line slope in direction of flow and inverted trap is not necessary with a single riser.

  4. Likes supers_5 liked this post.
  5. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Evaporator below the condensing unit gets a trap at the bottom and a inverted trap at the top.

    Download
    DuPonts best piping practices.

  6. #5
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Evaporator below the condensing unit gets a trap at the bottom and a inverted trap at the top.

    Download
    DuPonts best piping practices.
    That's an consequential inverted trap only because a riser the height of the coil is recommended to prevent floodback/flooded starts in cases of power failure and non-pumpdown circuits.

  7. Likes Tjune54 liked this post.
  8. #6
    Join Date
    Jan 2005
    Location
    steeler nation
    Posts
    2,414
    Post Likes
    Follow manufacturers recomendations

  9. #7
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    There are inverted traps on liquid lines too. Not really relevant to this conversation. But there you go.

  10. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Duponts book lists several combinations

  11. #9
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Duponts book lists several combinations
    DuPont’s one of the better guides. There is a lot of incomplete, conflicting & inaccurate information out there, vendor and manufacturers.

    I wrote the McQuay/ Daikin requirements for chiller products and edited their piping application guide. It’s the best and most complete I’ve seen for comfort & chill water applications. Included a number of recommendations not commonly listed. Ashrae included minimum capacity tables for oil return ~ 1990 that make a big difference in reliability and proper pipe sizing. Included liquid line check/relief arrangements and restricted double risers before any other mfg’s followed suit.
    Also reviewed hundreds of proposed and installed drawings & installations for McQuay/Daikin, Dunham Bush & Lennox. Very seldom would get a clear isometric drawing with all components and tie-ins.

    Note differences in Trane scroll recommendations re traps and horizontal line slope. Logic based on probable short cycling. Think better to prevent short cycling.

  12. #10
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Not really a trap. The suction piping was run above the coil when the evap was higher than the compressor..
    Like a trombone. The idea was if the coil flooded because of migration, the riser would contain the refrigerant
    and keep the compressor from slugging.
    Maybe 15-20 years ago Carrier sent a bulletin around saying it didn't do what they thought.
    The systems can migrate too much refrigerant for the riser to contain it. Instead they recommended a liquid line
    solenoid to open on start up. Not a pump down, that's another topic. Just a valve to stop migration.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  13. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Quote Originally Posted by hvacker View Post
    Not really a trap. The suction piping was run above the coil when the evap was higher than the compressor..
    Like a trombone. The idea was if the coil flooded because of migration, the riser would contain the refrigerant
    and keep the compressor from slugging.
    Maybe 15-20 years ago Carrier sent a bulletin around saying it didn't do what they thought.
    The systems can migrate too much refrigerant for the riser to contain it. Instead they recommended a liquid line
    solenoid to open on start up. Not a pump down, that's another topic. Just a valve to stop migration.
    OP's talking Cooler Freezers, not comfort cooling.

  14. #12
    Join Date
    Sep 2021
    Location
    Gulf Coast FL
    Posts
    17
    Post Likes
    No; not for down flow suction. All it would do would be to increase the pressure drop by three 90's worth.


    Quote Originally Posted by NotThatBright View Post
    If your condenser is located below your evaporator is there any point to an inverted P trap at the top of the riser in the suction line? Working on some coolers/freezers and the installation manual calls for suction line traps every 15ft in the riser (which I understand) and an inverted trap at the top of the walk in box and I just didn't quite understand why.

  15. #13
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Quote Originally Posted by pecmsg View Post
    OP's talking Cooler Freezers, not comfort cooling.
    Same function. His manual called for an inverted trap where some call it a riser & return. Same idea of not slugging.
    Technically it's not a trap because it doesn't trap.
    A solenoid does the same function but is more fail safe as the riser might not prevent slugging.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •