    Oil Cleanup/ Burnouts

    So did a conversion of an old r22 system over to 407c and when performing the oil change the drain filter came out totally plugged, oil was black lookin like old motor oil. So in this instance when putting in new filter cores I used the HH cores for clean up and made a note to do a second change here in the next couple of weeks but I was curious what procedures anybody else would follow when encountering bad oil. Name:  IMG_20210819_112949157.jpg
Views: 361
Size:  2.07 MBName:  IMG_20210630_133512706.jpg
Views: 354
Size:  2.51 MB

  2. #2
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Is that the oil "screen" from the comp oil sump? What oil is in the comp? Do an Acid Test of the oil. Change the oil. Add a Changeable Core SL&LL FD's and retest after just a few days, not weeks. The oil and FD might have to be replaced a few times. Got a SGMI on this? What condition is the Cond Coil in?

  3. #3
    Join Date
    Sep 2013
    Location
    Wi
    Posts
    1,026
    Post Likes
    keep changing it till it stays clean.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Those filters are going to plug up quickly with POE in the system, it acts as a cleaning agent inside.

    Oil like that have a compressor handy, you'll be changing it shortly.

  5. #5
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    You better put a suction filter on that system FAST.....that POE is gonna return every bit of crap from out in the system.

    From the looks of that screen, You'll be putting another compressor in if you don't stay on top of it.

    Make sure you have at least 20* at the compressor also.

  6. Likes R600a liked this post.
  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    FWIW
    Copeland does not recommend POE in those compressors. I’ve seen 2 fail shortly after converting to POE. Not done by us and NO suction filter.

  8. Likes dieseldude liked this post.
  9. #7
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    This is EXACTLY why I don't convert old systems to 407c.
    If it didn't have poe to start with it's either staying 22 or going to a drop in like mo99 that doesn't require an oil change.
    And even using a drop in, I add a suction filter.
    This system was already on it's way out by the look of the oil. The fingers will be pointing at the last guy to touch it.

  10. #8
    Join Date
    Mar 2021
    Location
    Cen Cal
    Posts
    111
    Post Likes
    Thread Starter
    Ya I'm aware of the possible problems with a 407c conversion and the customer was made aware before the job began but comparing the price of 200lbs of r22 vs 407c in todays world for a system that probably won't make it another 10 years regardless of what we put in it, that was the choice. the story with this place is an old customer of my current company acquired this building recently and they wanted it up and running. We committed to that with no warranties so if fingers are pointed no worries.

  11. #9
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Quote Originally Posted by pecmsg View Post
    FWIW
    Copeland does not recommend POE in those compressors. I’ve seen 2 fail shortly after converting to POE. Not done by us and NO suction filter.
    Interesting, doesn't every new recip. Come with POE now?

  12. Likes toptech liked this post.
  13. #10
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Quote Originally Posted by TheReefer View Post
    Ya I'm aware of the possible problems with a 407c conversion and the customer was made aware before the job began but comparing the price of 200lbs of r22 vs 407c in todays world for a system that probably won't make it another 10 years regardless of what we put in it, that was the choice. the story with this place is an old customer of my current company acquired this building recently and they wanted it up and running. We committed to that with no warranties so if fingers are pointed no worries.
    Put a suction filter on, with a desiccant core, until it's cleaned up.

    Then make sure all your staging is working correctly, and you have correct superheat (at the compressor) during all stages of loading....that would give it a fighting chance to make it.

  14. Likes toptech liked this post.
  15. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Quote Originally Posted by 71CHOPS View Post
    Interesting, doesn't every new recip. Come with POE now?
    In the older ones.
    I’ll find the bulletin

  16. #12
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    I'll bet you this system is going to need 3-4 oil changes and FD swap outs and maybe 3-4 Acid Test Kits and some labor.

  17. #13
    Join Date
    Sep 2018
    Location
    Summerville SC
    Posts
    112
    Post Likes
    It’s likely not going to last long, but add acid away and multiple oil and drier changes,
    Check your superheat and adjust the txv to drop the temps , 407 will run higher with less capacity.
    You could Meg your changes to see if progress is being achieved?

  18. #14
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Got to ask, is there something nasty in the air there? Looks like not normal corrosion.
    HH suction cores clean up really well. Get a shell so they can be replaced easily. Usually more than one.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  19. #15
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Always a good idea to put isolation ball valves on the filters, so you can recover and easily change without pulling charge.

    If its a critical application, use two housings in parallel, so you can swap, and change filters without shutting the system down.

  20. Likes R600a liked this post.
  21. #16
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Quote Originally Posted by 71CHOPS View Post
    Always a good idea to put isolation ball valves on the filters, so you can recover and easily change without pulling charge.

    If its a critical application, use two housings in parallel, so you can swap, and change filters without shutting the system down.

    If you do valve a drier this way, or with a bypass, include a relief valve. Closing the valves to the driers and opening a bypass could result in a hydro-static burst if the liquid refrigerant built up pressures and having no where to go. This might happen if the drier was restricted and the bypass was opened and left that way.
    I used to run in to driers piped w/o a relief. I thought at the time it was the way to pipe them until I ran across a relief valve requirement
    in a spec. After thinking about it I began to include them on the drier.
    Just a thought.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  22. #17
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Very good point.

    Another way to do it is to either leave the unused housing in a vacuum and isolated until needed.

    Or you can close the upstream valve, but leave the downstream valve open on the unused housing. Then just open the upstream valve when you're ready to put it into service.

  23. #18
    Join Date
    Sep 2021
    Location
    Gulf Coast FL
    Posts
    17
    Post Likes
    First drain? Or an oil change after the first one?

    If first: what do the condenser coils look like? Is there a HP safety? Is it manual or automatic reset?




    Quote Originally Posted by TheReefer View Post
    So did a conversion of an old r22 system over to 407c and when performing the oil change the drain filter came out totally plugged, oil was black lookin like old motor oil. So in this instance when putting in new filter cores I used the HH cores for clean up and made a note to do a second change here in the next couple of weeks but I was curious what procedures anybody else would follow when encountering bad oil. Name:  IMG_20210819_112949157.jpg
Views: 361
Size:  2.07 MBName:  IMG_20210630_133512706.jpg
Views: 354
Size:  2.51 MB

  24. #19
    Join Date
    Sep 2021
    Location
    Gulf Coast FL
    Posts
    17
    Post Likes
    What are the two lines connected to that external U-bend ?


    Quote Originally Posted by TheReefer View Post
    So did a conversion of an old r22 system over to 407c and when performing the oil change the drain filter came out totally plugged, oil was black lookin like old motor oil. So in this instance when putting in new filter cores I used the HH cores for clean up and made a note to do a second change here in the next couple of weeks but I was curious what procedures anybody else would follow when encountering bad oil. Name:  IMG_20210819_112949157.jpg
Views: 361
Size:  2.07 MBName:  IMG_20210630_133512706.jpg
Views: 354
Size:  2.51 MB

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •