    Confused Voltage Spikes Causing VRF Issues

    Does anyone know what type of surge protection devices you have used for Mitsubishi Electric VRF? There is a variance of 5%, but also states any voltage above 5 Volts will cause error code 4250 which is a over current protection. After 3 times, the system shuts down. Just need some type of voltage surge suppressor to keep the voltage spikes from damaging the inverter board. Any help is appreciated.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Voltage “Should” be within 10% of rating. 5% won’t cause an issue.
    ICM makes good products

  3. Likes RichcoolTex liked this post.
  4. #3
    Join Date
    Aug 2021
    Posts
    3
    Post Likes
    Thread Starter
    Thanks, Pecmsg. My problem is that we are constantly having voltage spikes, and could end up ruining the Inverter Board on the VRF ODU. I will look up ICM. Thanks!!!