Thread: Service port location for sub cooling

  1. #1
    Join Date
    Aug 2021
    Location
    Illinois
    Posts
    1
    Post Likes

    Service port location for sub cooling

    York split system condenser 10 ton single circuit tandem compressor.
    I noticed the high side service port is located on the discharge of the compressor as opposed to outlet of condenser coil. I thought sub cooling pressures and temperatures should be read when the refrigerant is in a liquid state. I have also seen this port placement on packaged rooftops, is the only requirement when reading high side pressure is that it is after the compressor and before the metering device? Does it matter that pressure is read when the refrigerant is in a high pressure vapor state as opposed to high pressure liquid so long as temp is read at outlet of condenser coil?

  2. #2
    Join Date
    Mar 2015
    Location
    Canada
    Posts
    1,703
    Post Likes
    There's a few psi drop over the piping and Condensor. Usually not enough to even subtract from your readings, since it's under 1%

  3. Likes ksefan liked this post.
  4. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Typically, the pressure drop is not going to be much, unless you have issues like: overcharge, undercharge, non-condensibles, mixed refrigerant, dirty coils, changes in refrigerant flow rates (multiple compressors, unloaders, bad valves, etc), low evaporator airflow, plugged filter/driers, metering device issues, etc. As long as you never have those issues, you won’t need a liquid line port.

  5. Likes heatingman liked this post.
  6. #4
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Commercial chillers may have 10-35 psid. Most smaller condensers have 3-10 psid. Check the ref tp chart and may be ~2* sat dif @ 10psid. Often the vendors will have charging charts instead of stating liquid subcooling number for charging. Would always add service ports if opening a system.

  7. Likes CEAS-AC-TECH liked this post.
  8. #5
    Join Date
    Sep 2018
    Location
    Metro Detroit
    Posts
    26
    Post Likes
    Quote Originally Posted by ehsx View Post
    Commercial chillers may have 10-35 psid. Most smaller condensers have 3-10 psid. Check the ref tp chart and may be ~2* sat dif @ 10psid. Often the vendors will have charging charts instead of stating liquid subcooling number for charging. Would always add service ports if opening a system.
    Agree. A 3-10 psi difference with r22 would be .7F-3F off. for r410 it would be 6.-2F off. so maybe you wouldn't charge by it but you could get a rough idea if there was adequate subcooling.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •