    Question code compliant or not - "romex" in conduit

    Is it permissible to use NMC/Romex in conduit, like for an a/c whip?

    I was told no by our senior sparky and an inspector years ago, but have since heard it is okay per NEC. I did some reading in the section someone quoted, but I a not sure that applies: NEC code 334.15 .

    Thanks

    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  2. #2
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    I don't think so only in underground conduit.

  3. #3
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    5,598
    Post Likes
    I see it done almost universally, could just strip off sheathing if concerned about it.

    last inspection inspt commented can't bundle a bunch of wires through a 1 1/2" romex clamp in panel now.
    Col 3:23


    questions asked, answers received, ignorance abated

  4. #4
    Join Date
    Sep 2013
    Location
    Wi
    Posts
    1,026
    Post Likes
    not approved for damp locations . even though the cable contains thhn wire it is not marked

  5. Likes kangaroogod liked this post.
  6. #5
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    Quote Originally Posted by Galt View Post
    not approved for damp locations . even though the cable contains thhn wire it is not marked
    You're referring to with the jacket removed correct ?

  7. #6
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    No can do. I will sleeve it in a couple feet to a disconnect but even that is not code compliant

    Sent from my SM-N960U using Tapatalk
    ...

  8. #7
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    In a pinch .... Strip off the yellow ... or orange sheathing , and the paper ofcourse , so you only have the wires , and I doubt anyone would notice the difference

  9. #8
    Join Date
    Jun 2014
    Location
    Or
    Posts
    57
    Post Likes
    A few years ago a State Fire Marshall said it was not approved. He said something about the jacket on the romex acting like insulation if the wires got warm when inside conduit.

  10. #9
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    5,598
    Post Likes
    what does he say about wires in an insulated wall cavity? or under 16" insulation in attic? or buried in sparyed foam in wall?

    in attic or close to roof on top, you actually have to derate wire in some cases, or if more than one circuit run in a conduit. inspect was being a butt in one area so checked all that stuff on a job cust later backed out on.
    Col 3:23


    questions asked, answers received, ignorance abated

  11. #10
    Join Date
    Sep 2005
    Posts
    58,704
    Post Likes
    I vaguely remember something about the insulation on stranded single conductor wire has a different type of insulation than the single core wire in 'romex'... something about the insulation on the single conductors in romex is more vulnerable to snagging and shorting.

    You electrical guys... is that part of the code or no????
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  12. #11
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    Quote Originally Posted by pacnw View Post
    Is it permissible to use NMC/Romex in conduit, like for an a/c whip?

    I was told no by our senior sparky and an inspector years ago, but have since heard it is okay per NEC. I did some reading in the section someone quoted, but I a not sure that applies: NEC code 334.15 .

    Thanks

    NO, it specifically stats in the code you cannot use NM cable in wet locations and yes inside the conduit is considered a wet locations if used outdoor.

  13. #12
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Quote Originally Posted by VTP99 View Post
    NO, it specifically stats in the code you cannot use NM cable in wet locations and yes inside the conduit is considered a wet locations if used outdoor.
    Yup, not allowed outdoors for the reasons you say 300.9, 310.10, but along with that,NM is only rated for
    60degC, 140degF a conduit in the sun could get hotter than that and the allowable ampacity can't exceed that
    of a 60degC wire. Got to use a wire with a "W" in it's ID.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •