    Getting confused on Ranco ETC Differential setting for walk in cooler

    If you want to keep a walk in cooler at 35 f what would you set the Differential setting to? I know in cooling mode the Differential setting is above set point. Would you have the Differential setting at 2? or would you have the set point below 35?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,728
    Post Likes
    Are you measuring air or coil temperature?

  3. #3
    Join Date
    Jul 2009
    Location
    new york
    Posts
    928
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Are you measuring air or coil temperature?
    Air temp

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,728
    Post Likes
    Quote Originally Posted by bwd111 View Post
    Air temp
    Make it a coil temperature then you have a chance.

    I Like A12-701 but others swear by A12-700

  5. #5
    Join Date
    Jul 2009
    Location
    new york
    Posts
    928
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Make it a coil temperature then you have a chance.

    I Like A12-701 but others swear by A12-700
    I would but the old one burned out and that’s what the owners of the Mcdonald’s want on their cooler. I couldn’t see the old settings so I was thinking of letting it down to 34 with a 3° differential

  6. #6
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    I do 34°f with a 6°f differential
    Averages out around 37°f

  7. #7
    Join Date
    Jul 2009
    Location
    new york
    Posts
    928
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    I do 34°f with a 6°f differential
    Averages out around 37°f
    5 is the max. I was thinking with a cooler it’s not going to take that long to freeze because it’s been running since Friday at 4 o’clock and still barely any frost on the coil

  8. #8
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    The more differential the longer the off cycle = longer air defrost time.

  9. Likes R600a liked this post.
  10. #9
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    I've also set them at 30°f and a 10°f differential to average out at 35°f

  11. #10
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Quote Originally Posted by bwd111 View Post
    5 is the max.
    Per McDonald's ?
    Attached Images Attached Images  

  12. #11
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    I'm guessing what they really want is the product at 35*F. So that is where you put the stat, cut in at 38*F. The idea is that the product will hold temp a lot longer than the air temp, so typically the refrigeration will kick back on before the product rises one degree. Of course, you will likely need a time clock to turn off the refrigeration to assure no ice ups.


    Quote Originally Posted by bwd111 View Post
    If you want to keep a walk in cooler at 35 f what would you set the Differential setting to? I know in cooling mode the Differential setting is above set point. Would you have the Differential setting at 2? or would you have the set point below 35?
    I do a triple evac with nitro to remove non condensables.

  13. #12
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,728
    Post Likes
    Quote Originally Posted by bwd111 View Post
    I would but the old one burned out and that’s what the owners of the Mcdonald’s want on their cooler. I couldn’t see the old settings so I was thinking of letting it down to 34 with a 3° differential
    Thats what he wants then he can tell you what set points to use!

  14. #13
    Join Date
    Jul 2009
    Location
    new york
    Posts
    928
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Thats what he wants then he can tell you what set points to use!
    Exactly! But they don’t know and it’s the most ridiculous demands they have. I’m setting it at 35 with 6 diff and calling it a day

  15. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,728
    Post Likes
    Quote Originally Posted by bwd111 View Post
    Exactly! But they don’t know and it’s the most ridiculous demands they have. I’m setting it at 35 with 6 diff and calling it a day
    for 50 bucks throw a A12 inside. Cheap insurance to prevent the freeze ups your going to experience!

  16. Likes R600a liked this post.
  17. #15
    Join Date
    Jul 2009
    Location
    new york
    Posts
    928
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    for 50 bucks throw a A12 inside. Cheap insurance to prevent the freeze ups your going to experience!
    I just picked one up at RSD. Thanks for the info

  18. #16
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,728
    Post Likes
    Quote Originally Posted by bwd111 View Post
    I just picked one up at RSD. Thanks for the info
    Mount it inside the blower and wire it in series!

  19. #17
    Join Date
    Aug 2019
    Posts
    83
    Post Likes
    Set the box temp for 34 with a 6 degree differential or the unit will freeze up.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.