Page 2 of 2 FirstFirst 12
Results 21 to 29 of 29

Thread: Converting walk-in compressor to digital controls

  1. #21
    Join Date
    Sep 2012
    Location
    Utah, USA
    Posts
    18
    Post Likes
    Thread Starter
    Quote Originally Posted by WT70 View Post
    Let me do some research.

    So basically send the BAS the alarm.


    Sent from my iPhone using Tapatalk
    Exactly. Dry contacts would be enough. Thanks!

  2. #22
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,611
    Post Likes
    Quote Originally Posted by Pandelerium1138 View Post
    Yes, all of the above. Off cycle defrost for the medium temp walk-ins, electric defrost for the low temp walk-ins. We can use BACnet or LonWorks, but I would rather the alarms were integral to the system, not generated by the BAS system, since I would have to have our controls guys and/or Staefa BAS contractor figure out the logarithm, and that could get messy. I don't know if there is enough need out there for this kind of system to make it commercially feasible, but there's got to be some, especially morgues. Our morgue uses a MorTech system for lead/lag and alarming that is far less than adequate, and it's only just over a year old. Even the installer hated it. I have looked far and wide, there just isn't anything "plug and play" out there. Some have taken Pelican HVAC systems and modified it to work on a walk-in, but it's far from perfect, and highly experimental. Not something I would use on a morgue. Master-Bilt came up with a controller along these lines, but they are problematic. I know, I have one in another building, it's rather finicky. It needs to be robust, and able to function independently even when the BAS goes down. An option for cloud monitoring with a wireless gateway would be great for customers that do not use any kind of BAS, that would increase the customer base dramatically. Maybe just a standard dry contact for any alarm system and a separate add-on interface for those that want one.
    Let me do some research.

    So basically send the BAS the alarm.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  3. #23
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    33,589
    Post Likes
    Hell you can put pressure sensors on everything, the BMS will monitor it all!

  4. #24
    Join Date
    Mar 2021
    Location
    Cen Cal
    Posts
    26
    Post Likes
    Quote Originally Posted by Pandelerium1138 View Post
    The condensers came with Copeland High/Low pressure controls and those have separate contacts for High and low pressure, those will work. The ones that have been replaced with Johnson Controls pressure controls do not, I would have to replace them back to the Copeland controls, which seem to have a high failure rate. I agree, simpler is better in some cases. I can have the relay tied into our Staefa BAS, I'm thinking all the relays in series so there's only one alarm, and idiot lights to tell the building operators which one, so when they call me at 2 am, I can tell them if it's redundant, send me a work order and I'll deal with it in the morning -or- have to drive in.

    Someone should come up with a digital compressor control system that talks wirelessly to a remote pump down thermostat that controls a solenoid or LEV, uses transducers and thermistors along with a logarithm to determine if and when there's a problem, put the whole thing online with alerting and drag the refrigeration industry kicking and screaming into the 21st century. Online temperature monitoring in the box is useless at telling when system A is down when system B is running fine on a redundant system. Until system B also fails, then you have an emergency that was supposed to be avoided with redundancy. Yes, this is much more complicated, but in some instances a needed option. The reason I bring this up, if a kitchen walk-in goes down, some food might be lost. If our morgue walk-in goes down, it's a whole different story (especially during a pandemic). Yep, I got called in at 9 PM once on just such a call and it sucked. Especially since a contractor that was working on system A under warranty screwed up and turned off the wrong disconnect outside. With this kind of system I would probably have been alerted before I got to the parking lot, not 3 hours later when the box temp went into alarm.
    what exactly is the point of this. Are you trying to be alerted of a specific component failure or just being alerted of a system failure sooner. I think everyone gets all gung hoe on controls but remember it doesn't make the system anymore reliable and it makes it that much harder for another guy to come by and figure what its doing when it does fail. I would imagine a box temp alarm along with regular inspection of an up to date system would have a fairly low failure rate.

  5. #25
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    33,589
    Post Likes
    Quote Originally Posted by Pandelerium1138 View Post
    I have several water cooled walk-in compressors for walk-ins on a rack for our kitchen and cafeteria. They are all Copeland, a couple Discus, the rest regular semi-hermetic. They currently have mechanical controls, the standard high/low pressure switch and the overload on the compressor. The issue is, there's no way to tell if they are tripped on high head (other than our online temperature monitoring in the box itself). I was looking onto converting to a digital system like the Emerson EUC or something similar. I cannot find a retrofit anywhere. Any ideas? Thanks!
    Water cooled equipment gets Manual Resets.

    Problem solved!

  6. #26
    Join Date
    Sep 2012
    Location
    Utah, USA
    Posts
    18
    Post Likes
    Thread Starter
    Quote Originally Posted by TheReefer View Post
    what exactly is the point of this. Are you trying to be alerted of a specific component failure or just being alerted of a system failure sooner. I think everyone gets all gung hoe on controls but remember it doesn't make the system anymore reliable and it makes it that much harder for another guy to come by and figure what its doing when it does fail. I would imagine a box temp alarm along with regular inspection of an up to date system would have a fairly low failure rate.
    You are right, it doesn't increase reliability. However, if you have a very critical system that has redundant systems, you need to know when one of them goes down, preferably before the other one does. Sometimes getting all gung ho on controls and trending/alerting has a purpose. Yes, I am trying to get alerted when specifically one of the redundant systems go down, or has a trending pattern indicating an imminent failure. We perform scheduled maintenance on these every quarter. However, everything man makes will break eventually. Especially the new crap on the market today.

    Sent from my SM-G960U using Tapatalk

  7. #27
    Join Date
    Sep 2012
    Location
    Utah, USA
    Posts
    18
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Water cooled equipment gets Manual Resets.

    Problem solved!
    Has manual resets. Problem not solved, redundant system takes over, no one knows.

    Sent from my SM-G960U using Tapatalk

  8. #28
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    33,589
    Post Likes
    Several controls have a SPDT Switch, wire the second contact to BMS, horn, light.

    Simple is better!

  9. #29
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,611
    Post Likes
    Quote Originally Posted by Pandelerium1138 View Post
    Has manual resets. Problem not solved, redundant system takes over, no one knows.

    Sent from my SM-G960U using Tapatalk
    So here is what I have come up with.

    Each unit will monitor suction and discharge, lock out and alarm on high pressure.

    One temp sensor will be discharge temp, one will be case temp.

    Will alarm if either sensor is above setpoint for a set amount of time.

    Alarming out: each controller will have an alarm out. You can tie an individual controller alarm out relay to its own alarm input for the BAS, this would alert whoever “unit #” was down.

    Or you could have a single alarm to BAS that just says “refrigeration alarm”, wired through NC relays.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..