    Mcquay centrifugal chiller not starting due to low oil Delta temperature

    Hello 👋 Everyone
    Mcquay centrifugal chiller not starting due to low oil Delta temperature 🌡️

    What is the problem
    Last edited by Papai Santra; 07-15-2021 at 11:18 AM. Reason: Miss spelled

  2. #2
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Oil must be ~ 30*f above evap saturated.

    Usually occurs on morning start up when warmer bldg water returns to chiller. Heater has to raise oil sump temp before starting.

    Start cw pumps earlier, check oil sump heaters.

  3. #3
    Join Date
    May 2019
    Location
    Kolkata
    Posts
    42
    Post Likes
    Thread Starter
    Thanks