    R404 walk in

    I’m n ac guy trying to help a buddy with walk in with r404. Can only get 20 degrees super heat liquid temp 112. 305 psi. Suc 50 psi. This is a new start up Txv is open all the way. Site glass is full amp 17 amp rated 22. Outdoor temp 82 box 45

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    20* where. At the compressor fine at the coil no good.
    Is this a pressure limiting valve?
    Can’t accurately adjust until at or near temperature.

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Just read
    Put the damn valve back at mid point.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes

  5. #5
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    2,521
    Post Likes
    FYI you check superheat when box is close to temp 50psi sounds low for med temp 404
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  6. #6
    Join Date
    Jul 2021
    Posts
    6
    Post Likes
    Thread Starter
    24 degrees at compressor

  7. #7
    Join Date
    Jul 2021
    Posts
    6
    Post Likes
    Thread Starter
    Box is 45

  8. #8
    Join Date
    Mar 2016
    Location
    NY
    Posts
    415
    Post Likes
    Quote Originally Posted by Rleymarie View Post
    Box is 45
    Walk in cooler or freezer?
    “Happiness can be found, even in the darkest of times, if one only remembers to turn on the light.”
    "Ha! Memory is RAM!"

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Quote Originally Posted by Rleymarie View Post
    24 degrees at compressor
    24 suction temp or SH?

  10. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    And reset that valve to mid point.

  11. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Sounds like your TXV is too small if you have it turned wide open and still only have 50 psi

    Ive seen it before ...

    Whats the number stamped on the valve ?

    Make sure the Nozzle was put in also

  12. #12
    Join Date
    Jul 2021
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by Bombboy90 View Post
    Walk in cooler or freezer?
    walk in cooler 24 degrees super heat at compressor -- txv is full open

  13. #13
    Join Date
    Jul 2021
    Posts
    6
    Post Likes
    Thread Starter
    sporlan SBQE w/external equalizer -- pink cartridge --- sporlan sized -- site glass is full -- what type head pressure this run at 90 degree out door box at 45

  14. #14
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    Quote Originally Posted by Rleymarie View Post
    sporlan SBQE w/external equalizer -- pink cartridge --- sporlan sized -- site glass is full -- what type head pressure this run at 90 degree out door box at 45
    At 90 f 300psi wouldn't surprise me depending on condenser efficiency.
    350 probably wouldn't even be completely out of line....
    But obviously the lower the better.
    Pulling down a hot box will have elevated head pressure. If it's not tripping a safety then I rarely read head pressure until the box is down to temperature on a new install.
    After the box is down to temperature, then you start measuring superheat and head pressure. Until then you are wasting time.

  15. Likes flangatang7 liked this post.
  16. #15
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,525
    Post Likes
    Moved to Refrigeration forum

  17. #16
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Without knowing the box size, compressor size, evaporator size " pink cartridge " means nothing.
    Well other than it's rated at 1.5 ton.

  18. #17
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by Rleymarie View Post
    I’m n ac guy trying to help a buddy with walk in with r404.
    Cooler or Freeer?

    Can only get 20 degrees super heat liquid temp 112. 305 psi. Suc 50 psi. This is a new start up. Txv is open all the way. Site glass is full amp 17 amp rated 22. Outdoor temp 82 box 45
    None of this tells us anything without the following:

    Box size

    Evaporator Model

    Condensing unit model (not compressor)

    You gave use the TXV size, as 1.5 ton based on how it’s built. But what power element, and why a SBQE instead of an SQE? I personally do not use balanced port valves except for a purpose that specifically calls for it (eg, flooded evap, some ice machines, smaller single pass evaps) but that is my preference.

    Liquid/Suction line sizing.

    Suction pressure at the condenser

    Suction pressure at the Evap.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  19. #18
    Join Date
    Jul 2021
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by BadDaddy420 View Post
    Cooler or Freeer?



    None of this tells us anything without the following:

    Box size

    Evaporator Model

    Condensing unit model (not compressor)

    You gave use the TXV size, as 1.5 ton based on how it’s built. But what power element, and why a SBQE instead of an SQE? I personally do not use balanced port valves except for a purpose that specifically calls for it (eg, flooded evap, some ice machines, smaller single pass evaps) but that is my preference.

    Liquid/Suction line sizing.

    Suction pressure at the condenser

    Suction pressure at the Evap.


    Sent from my iPhone using Tapatalk

    3/8 liquid line
    7/8 suction
    box 12 x 24 x 8
    50 psi at compressor
    condenser AVA7523ZXNXC 3 HP TECHUMSA
    EVAP CEL0250AS6AMAB0000 HEAT CRAFT

    A LITTLE HISTORY -- WHEN I ARRIVED IT HAD A SBQ BODY WITH INTERNAL EQUALIZER , KT43JC ELEMENT AND A C CARTRIDGE --- CALLED SPORLAN GAVE ALL INFO THIS IS WHAT I GOT

    SBQE BODY
    KT43SC/PC ELEMENT
    B CARTRIDGE

    IT SEEMS THE EVAL IS STARVING ???

    7 DEGRTEES TD ACROSS COIL

    DID NOT CHECK SUCTION AT EVAP

  20. #19
    Join Date
    Sep 2016
    Location
    PL In New York
    Posts
    952
    Post Likes
    I'm anxious to know what the problem was. Does it make temperature and shut off eventually? How far is the CU from the evap? Above or below?

  21. #20
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes

    R404 walk in

    Quote Originally Posted by Rleymarie View Post

    3/8 liquid line
    7/8 suction

    This should be fine.

    box 12 x 24 x 8

    Btu Required is 12,960 with heavy use.

    EDIT: That was off US Cooler’s website. The HeatCraft chart states around 20,000btu. So that’s sized correctly as well.


    50 psi at compressor

    This is, if I remember, about a 5deg sst. That’s too low. I’ll get to what’s up. I think.

    Condenser AVA7523ZXNXC 3 HP TECHUMSA

    Capacity 21,460btu

    EVAP CEL0250AS6AMAB0000 HEAT CRAFT

    Capacity 25,000btu

    A LITTLE HISTORY -- WHEN I ARRIVED IT HAD A SBQ BODY WITH INTERNAL EQUALIZER , KT43JC ELEMENT AND A C CARTRIDGE --- CALLED SPORLAN GAVE ALL INFO THIS IS WHAT I GOT

    SBQE BODY
    KT43SC/PC ELEMENT
    B CARTRIDGE

    This is a 1 1/2 - 2 ton Balanced port External EQ

    IT SEEMS THE EVAL IS STARVING ???

    7 DEGRTEES TD ACROSS COIL

    DID NOT CHECK SUCTION AT EVAP
    Install a SQE 3x4x2 with a Black/#5 cartridge and a KT43SC power element (which you have).

    I believe that will solve your problem. I honestly do not think the balanced port will open up enough with the cartridge that is in it.

    I’d suggest going with the White C cartridge for the balances port you have, but I don’t know if it will throttle down enough when the box gets to temp and load is down.

    Someone else may disagree. But that’s my pennies worth.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •