Results 1 to 11 of 11
Thread: Troubleshoot with me
    Jul 2019
    Montana
    Outdoor air temp: 78
    Return wet bulb: 54
    Supply air temp: 50
    Return air temp: 65
    Attached Images Attached Images
    Jul 2019
    Montana
    EVAP freezing up, found the txv bulb was uninsulated, no change after insulating
    Jul 2013
    Richmond, VA
    Restricted TXV.
    Although on some Goodmans they are adjustable, so you may want to try that if it can be. Most are not, in which case replace it.
    Edit: I took my comment back about low charge in addition to the TXV. I noticed your return temp is low, which would result in low sub cooling. Still, the higher than normal SH indicates a restriction.
    Everything Im going to say today are my conclusions and my opinions, my opinions are based on my education, my training, my experience. Different people have different experiences, so they have different opinions and I make no claim that my opinion has its origin in the mind greatness. - Paul Harrell
    Mar 2015
    Medford, N.Y.
    What do you think is wrong? What i room temp?
    Jan 2010
    Sea to Sky
    No load and no low ambient controls....
    Sent from my SM-G965W using Tapatalk
    Jan 2015
    San Diego, CA
    Agee with the Restricted TxV diagnosis.
    Mar 2018
    Kansas Flatlands
    Quote Originally Posted by szw21 View Post
    me too
    Jul 2019
    Montana
    Restricted txv is correct
    Oct 2011
    Chicagoland Area
    Return air 65*?
    Officially, Down for the count
    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
    Mar 2015
    Medford, N.Y.
    Quote Originally Posted by 2sac View Post
    Return air 65*?
    X2
    Virginia
    Probly had window Ac;s