    Late 1960's Reciprocating Compressors Discharge Temperatures

    Hi Folks,

    We have Fedders 3 ton unit running nicely for over 50 years made in the late 60's. The unit is a stand alone unit encompassing the compressor, condenser, evaporator, etc.. The squirrel fans are controlled by one 4-5 amp motor that circulates air internally and cools the compressor/condenser thru 16" intake/exhaust ducts. The system is clean. It is a sealed system with no access valves. It still runs nicely (R22). The input/output air over the evap has 20 deg drop when indoor temp is 80. The condensor mid-coil is roughly 30 deg above outside temp, the evap mid-coil is 38 below indoor temp.

    The problem with it was the low pressure switch on the suction line sometimes kicks in & cuts off compressor and when the temp outside goes up to the 80's, the discharge temp starts rising over 225. I asked you guys before and was told to have access valves put in by either recovering, having the valves brazed on, and then recharging and testing the system OR the other option was to use a "pinch-off" on a process stub to install access valves and then test. The tech that came said he could recover & install the valves, but was not familiar with the pinch-off. He was not too concerned with the discharge temp as the system may need charging.

    The question is were these reciprocating compressors made in the late 1960's designed to handle higher discharge temps or 225 is the max? How much can the discharge temp possibly drop if it needs some charge?

    The compressor has a process stub in good shape on the reciprocating compressor top side next to the suction line (discharge line is at the bottom). Can a pinch-off be used there for the suction side (metering is fixed capillary)? There are no process stubs on the suction line itself.

    Thank you
    Alan
    Attached Images Attached Images   

  2. #2
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,309
    Post Likes
    The compressors cover plate says internal and external overload instead of a just a internal one, like modern compressors seem to have in residential.

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Get the suction S H in line and the problem should go away!

  4. #4
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    Especially on something old I'd try and keep discharge under 180.
    Cleaning the condenser may be all you need to do to achieve this.
    The other thing is it may be a little low on charge. I'd be recovering and welding in proper access ports to get proper readings on sub cooling and superheat

  5. Likes R600a liked this post.
  6. #5
    Join Date
    Jul 2019
    Posts
    14
    Post Likes
    Thread Starter
    Quote Originally Posted by Bazooka Joe View Post
    The compressors cover plate says internal and external overload instead of a just a internal one, like modern compressors seem to have in residential.
    Hi Joe,

    External being the LPC. Good to know.

    Thanks
    Alan

  7. #6
    Join Date
    Jul 2019
    Posts
    14
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Get the suction S H in line and the problem should go away!
    Suction superheat was roughly 15 deg over target SH at the time. Hopefully just needs a charge & no issues with restriction on any of the 4 capillary tubes.

    Thanks
    Alan

  8. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Quote Originally Posted by Alan55 View Post
    Suction superheat was roughly 15 deg over target SH at the time. Hopefully just needs a charge & no issues with restriction on any of the 4 capillary tubes.

    Thanks
    Alan
    so what was your target SH?

  9. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Quote Originally Posted by Alan55 View Post
    Hi Joe,

    External being the LPC. Good to know.

    Thanks
    Alan
    A LPC is not an external overload.

  10. #9
    Join Date
    Jul 2019
    Posts
    14
    Post Likes
    Thread Starter
    Target SH 15.4...As I recall last time I checked with my brother on the elec schematic/circuit who is an EE found only the low and high pressure switches inline to cutoff the power outside the compressor...will ask again.

  11. #10
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    It is a sealed system with no access valves
    Suction superheat was roughly 15 deg over target SH at the time.
    Name:  06C04B3E-7C33-4D18-AC66-D084330EE2AC.jpeg
Views: 415
Size:  259.1 KB

    How does one determine system superheat with no access valves? What is under the yellow caps?
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  12. #11
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,309
    Post Likes
    Quote Originally Posted by Alan55 View Post
    Hi Joe,

    External being the LPC. Good to know.

    Thanks
    Alan
    External overload is not the LPC, there is a internal overload and the external one is behind the cover plate, reason why there is a built up area between the cover plate and the actual compressor skin. Been a while, since I worked on one, but the external one(s) may be a for sensing over amprege. Modern compressors have 3 power wires feeding compressor, your has more wires going into that cover plate.

    Easy enough to verify, shut power off and remove those three screws.

  13. #12
    Join Date
    Jul 2019
    Posts
    14
    Post Likes
    Thread Starter
    Quote Originally Posted by rider77 View Post
    Name:  06C04B3E-7C33-4D18-AC66-D084330EE2AC.jpeg
Views: 415
Size:  259.1 KB

    How does one determine system superheat with no access valves? What is under the yellow caps?
    Rider77

    "The condensor mid-coil is roughly 30 deg above outside temp, the evap mid-coil is 38 below indoor temp".....I got those temps using thermocouples....thats why i say roughly. The actual testing SH at that moment of time was using the specific WB, suction, evap, outdoors temps. Those yellow plastic caps cover the production service valves that are permanently sealed with pins....its not magic :-)

  14. #13
    Join Date
    Jul 2019
    Posts
    14
    Post Likes
    Thread Starter
    Thanks Joe...appreciate it.

  15. #14
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Put a piercing valve on the process tube and go from there.

  16. #15
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by rider77 View Post
    Name:  06C04B3E-7C33-4D18-AC66-D084330EE2AC.jpeg
Views: 415
Size:  259.1 KB

    How does one determine system superheat with no access valves? What is under the yellow caps?
    Measure the evaporator/cond temp on u tube in middle of circuit gives you saturation temp. Then you can figure SH/SC from there. Same way Trane RTAA Or Carrier 30GT chiller controllers measure it.

  17. #16
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Under the pecker head is very Crisp wires. Be careful
    SH at the pump still applies
    20 - 40* at the pump
    200 * discharge

  18. #17
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    Clean the coils and blower wheel. Don't touch the sealed system.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  19. Likes Bazooka Joe liked this post.
  20. #18
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    How far down the DIY road should we go in the AOP forum?
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  21. #19
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    It's been a month I think we reached the end of the road.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •