    New condenser pad installed on river rocks - is this stable?

    New installation over the winter. Professional installer. They never fired up the A/C when testing it because it was too cold outside (50F?), so they told me to call in the spring so they can come out and fire it up. I just called and they can't come out until August...

    So I went outside to inspect it and toy with the idea of just firing her up anyway and I noticed that many of the river rocks had already migrated out from under the pad. I took a level to it and it's not exactly level, either.

    This doesn't look stable, but what do I know? If it's not installed properly, I'd like to know how it should be installed before I call and complain.

    (Note it's a 2-ton condenser with an ultralight UC3636 pad).

    Thoughts?

    imgur.com/a/Q3C1izm

  2. #2
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    I think your fine.

    Waiting until August to fire it up is completely unacceptable

  3. Likes Mr Bill liked this post.
  4. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    August

    B S.
    Give me money back!

  5. #4
    Join Date
    Jan 2014
    Location
    New England/Florida
    Posts
    14,310
    Post Likes
    Good luck trying to start it up, it could easily be electrically deenergised with the service valves closed and just nitrogen as a holding charge in the lineset and indoor coil to keep system dry.

    Take a photo of the pad and send it to them, unreal they can’t get to the job till August. They should bend over backwards to get your unit up and running. Suggest calling the owner and tell him/her to get there as out here themselves instead of being on the golf course..

  6. Likes BaldLoonie liked this post.
  7. #5
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Since it's already installed, to be able to set the unit on anything different, they would probably have to remove it and reinstall it. What you could do, or have them do is, level the unit up, and pour some sort of concrete foundation around the existing pad, to hold it in place. Personally, I would not want to remove the unit and have the line-set open up, and possibly cause other issues "that could" happen during the reinstallation. Sometimes if your careful, and you can get enough help to lift it up and try and stable it up some that way. The underneath of that slab is foam, one might think the rocks would just eventually sink into the foam and self level, I do believe in miracles.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  8. #6
    Join Date
    Jul 2020
    Posts
    7
    Post Likes
    Thread Starter
    Thanks - yeah I'm not pleased about waiting and I plan on politely insisting they get someone out here just to make sure I can start it. It's going to be sweltering by August - humidity is no joke.

    I seriously know nothing about this stuff - we have chipmunks and squirrels galore and I'm worried that a rainstorm or a rodent's gonna knock just the right rock out and it's going to run off-kilter and I won't know about it until it breaks.

    Any job that deals with customers is pretty demanding and I don't wanna be "that guy," but if it needs to be fixed then I'd rather raise it now. If it should be fine I'll just leave it be. Like, should I ask them to look at it, or should I ask them to fix it? Or is it just fine as-is? There was a 2.5 ton on those rocks previously with a concrete pad that was removed when I had this one installed.

  9. #7
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Robear9992 View Post
    There was a 2.5 ton on those rocks previously with a concrete pad that was removed when I had this one installed.
    Name:  Head.gif
Views: 386
Size:  2.4 KB
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  10. #8
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    That's horsehockey. At our joint, we call our customers as soon as it is warm enough to check out the systems installed over the winter.

  11. #9
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,458
    Post Likes
    Yeah, August is unacceptable.

    I'm guessing you already paid in full?
    I do a triple evac with nitro to remove non condensables.

  12. #10
    Join Date
    Jul 2020
    Posts
    7
    Post Likes
    Thread Starter
    Quote Originally Posted by Mr Bill View Post
    Since it's already installed, to be able to set the unit on anything different, they would probably have to remove it and reinstall it. What you could do, or have them do is, level the unit up, and pour some sort of concrete foundation around the existing pad, to hold it in place. Personally, I would not want to remove the unit and have the line-set open up, and possibly cause other issues "that could" happen during the reinstallation. Sometimes if your careful, and you can get enough help to lift it up and try and stable it up some that way. The underneath of that slab is foam, one might think the rocks would just eventually sink into the foam and self level, I do believe in miracles.
    In your opinion, is this a proper installation? I ask because I'd like another opinion in case I have them come out and they're like, "No it's fine." I won't be like, "Well - MR BILL online said....", I'll just know enough to push back or, worst-case, hire someone else to come fix it.



    Quote Originally Posted by BBeerme View Post
    Yeah, August is unacceptable.

    I'm guessing you already paid in full?
    Yeah paid in full (financed through Carrier)

  13. #11
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    Ouch.
    A paid in full job, company financed, and they can’t be bothered to startup the unit until summer is nearly over?

    I can’t say what I’d do in an open forum...
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  14. #12
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    Maybe call carrier?
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  15. #13
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Robear9992 View Post
    In your opinion, is this a proper installation? I ask because I'd like another opinion in case I have them come out and they're like, "No it's fine." I won't be like, "Well - MR BILL online said....", I'll just know enough to push back or, worst-case, hire someone else to come fix it.
    Is it a proper installation? for us NO, but I've seen worse, so it might be for other companies. Looking at the way the copper runs to your unit, lifting it up to correct this, doesn't look like an option. I guess they just figured your old existing slab was on the rocks, that maybe the rocks were sentimental or something, we don't always know much of the history or reasons the previous installer did something. Here's my advise, if you don't like it, or your think it might be a future issue, call them back and ask them to correct it. Personally if they do come back to correct it, and have to remove the copper lines to fix it, I would be out there watching every move they make like a hawk, to be sure the lines are capped off or taped off during the fix, and they just don't allow them to lay in the rocks or on the ground, because regardless, they're NOT going to be happy, not happy can produce being sloppy, hope this helps.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  16. #14
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,117
    Post Likes
    Sorry, off subject but what is the deal with the vent pipe zig zagging up and away from the house. My gut tells me that there was a recirculation issue with the furnace exhaust. That is not the worst set up for the A/C I have seen but I would be calling and telling them that you will be starting the A/C on date "X" and if there is any reason that this should not be done they need to get out and fix it now.

  17. #15
    Join Date
    Jul 2020
    Posts
    7
    Post Likes
    Thread Starter
    Quote Originally Posted by BNME8EZ View Post
    What is the deal with the vent pipe zig zagging up and away from the house? My gut tells me that there was a recirculation issue with the furnace exhaust.
    The system I replaced was almost certainly DIY. It was a high-efficiency system and the intake / exhaust were reversed, dumping condensation back into my system. I mentioned this to the salesman who quoted my new system - to be aware that this would need to be addressed and work it into the quote. This is how they fixed it.

    I assumed it would be corrected indoors, closer to the unit, but this is how they did it. Since they technically met their obligation, it's just ugly, so I didn't complain. Starting to think I don't complain enough...

    I had issues right from the get-go. The gas wasn't installed properly and I had to call the FD when I smelled gas the night of the installation. It was bad, and when the gas company came out they said that it was leaking from multiple joints. They also forgot to remove the tab on the plunger from the condensation pump, so it never started up. The pan under the furnace was flooded, and they also didn't set up the bobber under the furnace to turn the furnace off if the pan fills with water. My basement almost flooded, but fortunately I caught it in time.

    The installers were young and I think it was 1/2 not knowing what they were doing and 1/2 trying to be as quick as possible. So I called the company and asked that they send someone senior out to inspect the system in addition to fixing it. The guy came out and didn't say anything about the installation outside.

    The company was Gem heating and plumbing (I didn't see anything in the rules against posting their name. If I missed it, I apologize and feel free to edit it out).



    Quote Originally Posted by Mr Bill View Post
    Here's my advise, if you don't like it, or your think it might be a future issue, call them back and ask them to correct it.
    Thanks - I'll probably do that.

  18. #16
    Join Date
    Feb 2013
    Location
    Sonora, California, United States
    Posts
    8,383
    Post Likes
    Im more concerned with the number of elbows on your furnace exhaust....

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •